Discuss 20amp switch on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

Simba1

-
Reaction score
0
Hi all,

I im in the process of rewiring a kitchen and as Im taking the old cable out etc.. I come across a 20amp double pole switch.
Looking for some answer..

1. it was on the kitchen ring ?

2. It was feeding a single socket behind were the oven once was but it was in 6mm cable from the switch to the socket ?

Thanks
 
Sounds like it was feeding an oven, not good practice!

But if it was a small oven (under 3kW) that came with a 13A plug then not an issue.

More commonly you see that for washing machines, fridge/freezer, etc, as an accessible means of isolation without pulling the thing out (which is often beyond a single person). It is not a requirement in the BS wiring reg, but in Scotland it is part of the building regs.
 
As pc said, sounds like it was feeding a cooker, but done badly.
Not really sure what your issue is though ? Surely if the kitchen is being rewired then all that crap will be stripped out and a new kitchen ring and cooker circuit will be installed properly ?
 

Reply to 20amp switch on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
969
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock