hi all, Got a question that i am not understanding correctly? Any body know how to work this out, I thought the answer was D, but apparently its A, According to the answer sheet. But i got my answer from page 63 bs7671.

An existing farmhouse and outbuildings are to be inspected and tested in order for the owner to comply with their insurer’s requirements

The lighting circuit in the hay barn is protected by a 5 A BS 3036 and a 300 mA RCD, the circuit has a measured Zs of 0.82 Ω.

The supply and installation forms part of a TN-C-S system.

What is the maximum measured earth fault loop impedance for the 5 A BS 3036 fuse?
  • A. 7.28
  • B. 9.10
  • C. 11.68
  • D. 16.80
 
Hi - I think you’ve looked at the distribution circuit table with 5 seconds disconnect, but this is a final circuit with 400ms dis time. Check Table 41.2 and since its measured in the field we assume it’s at 20 deg C and multiply by 0.8 factor. Hope that helps :) .
 
1. You used the wrong table. You used the table for a distribution circuit. The correct table is on the previous page.
2. You have apply the 0.8 factor for temperature at the time of measurement being less than the normal operating temperature.

Wilko beat me to it....
 
Well a whole host of wrongness...

1) It's a final circuit - so 5 secs disconnection time is wrong - must be 0.4 secs
2) even if you take this "correct" value - you have taken it from the DESIGN document - i.e whilst hot, the question states MEASURED - so either look the value up in an install document (OSG) or test document (GN3) - or correct for temperature - which is usually 0.8x the value from the design document.


So - I should have checked for other replies before posting ...........
 

Reply to 2391-52 question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
662
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
448
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock