2.
a) One part of the building has an area where chemical etching and washing down takes place.
i) List three factors which must be considered when inspecting the containment system in this particular area.
ii) Identify, for each of the factors given in (ai) above, the human senses that would best determine compliance.
b) The owner has agreed that the whole installation may be isolated in order for testing to be carried out. There has been period of one hour
allocated for this work.
List the tests that must be carried out during this period (individual circuits may be isolated after this period)
Another one for easy marks!
Its says chemical etching and washdown so
Suitabuity of containment so IP rating if there is water jets?
Suitability against corrosion? PVC conduit as metal rusts anc corrodes very fast
RCD protection as it will be a special location with water jets (think showers)
all the above is a visual inspection
Inspection and testing.
A true Ze,PFC,PSCC can only be done with main bonds disconnected so full shutdown.
Main bond resistance?
Full insulation resistance can be done if you follow section 2 of GN3 and disconnect imcomming Neutral. Connect line conductors together and test to the main earth point. Be wary of paralell resistances as it will drastically affect readings. It means you do not have to disconnect all lights and equipment suseptable to Insulation testing but has to be noted on limitations.