Discuss 2391 - would like to double check advice from tutor in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

C

chronyx

Would appreicate any clarification of what I have been told at college.

The tutor has told us to use 240V for calculations as this the output of a sub-station. Do you agree, or should I use standard 230V?

We were also told to remove the bonding conductor from the pipe clamp to test the continuity without parallel paths, but surely the logical thing is to disconnect at the board so that you also test the connection from the clamp to the pipe?

For those who remember the test board, am I right in assuming the MIMS cable sheathing earth is verified by the standard R1/R2?

How did you test the motor starter R1+R2 and insulation resistance values? Press in the contactor, or split the supply and load and test individually?

Cheers chaps :cheesy:
 
I would use 230, and did on my 2391

Disconnect bonding at the db

Yes r1+r2 is verified in the same way on mi

And I would be tempted to link out the contactor to be able to test r1+r2 at the motor

Hope this helps
 
it has been suggested to me that for the motor we measure method 1 to the contactor and use method 2 to measure R1 and R2 for the contactor to motor then add them all together.

I guess it all comes down to which is going to be quicker as they are all valid approaches. I suspect his checklist expects him to see method 1 on at least one circuit but after that I reckon it is your choice as long as it gets the right results.

And yes, 230V has been drummed into us, as has removing the bonding at the MET and measuring to the pipe, not the clamp.
 
I believe so. Basically treat it as 3 different circuits. Until you come to the IR test where you need to test all combinations of course.
 
If you get any questions that need voltage, other than one where you need to work it out, you will be given the voltage value.

i.e. You wont get a question starting like:- On a single phase supply. It will be worded, On a single phase supply with a nominal voltage of 230v, or words to that effect.

You may need to do volt drop calcs, but even then you will be told the voltage. The 2391 exam does not leave things open to interpretation.

Cheers.............Howard
 
Would appreicate any clarification of what I have been told at college.

The tutor has told us to use 240V for calculations as this the output of a sub-station. Do you agree, or should I use standard 230V?

We were also told to remove the bonding conductor from the pipe clamp to test the continuity without parallel paths, but surely the logical thing is to disconnect at the board so that you also test the connection from the clamp to the pipe?

For those who remember the test board, am I right in assuming the MIMS cable sheathing earth is verified by the standard R1/R2?

How did you test the motor starter R1+R2 and insulation resistance values? Press in the contactor, or split the supply and load and test individually?

Cheers chaps :cheesy:


You are worrying too much. You will be walked through the tests as part of the course, before you do the practical assessment. It doesnt matter how you do the tests, as long as you do them all, do them properly, and work safely.

Cheers............Howard
 
You are worrying too much. You will be walked through the tests as part of the course, before you do the practical assessment. It doesnt matter how you do the tests, as long as you do them all, do them properly, and work safely.

Cheers............Howard


I've done the course, and it was of limited use. Like I said, we were told how to do the bonding test incorrectly.
 
My exam is today, so having a revision session!

Would anyone be able to confirm what details can be obtained only by enquiry (From the DNO) rather than measurement?

I am thinking earthing arrangement and in some cases the supplier protective device.

Number of phases?

Ze, frequency, phase sequence, Ipf and voltage can all be measured.
 

Reply to 2391 - would like to double check advice from tutor in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
473
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Afternoon all. Apologies if this is a stupid question. I'm currently half part way through completing 2391 (second exam tonight) - so may be...
Replies
40
Views
4K
Hi, I'm an industrial spark and taking my 2391 next week (wish me luck, I need it). I decided to get a bit of practice and started an inspection...
Replies
43
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock