Discuss 24V LED Driver in the UK Electrical Forum area at ElectriciansForums.net

GerardPK

DIY
Reaction score
1
IMG_9065.jpg
 

Attachments

  • IMG_9049.jpg
    223.9 KB · Views: 15
  • IMG_9064.jpg
    210.4 KB · Views: 15
  • IMG_9051.jpg
    202.4 KB · Views: 13
Last edited:
As it states on the unit 'constant voltage' it should be possible to replace it with any constant-voltage 24V power supply unit rated for at least 8.4W or 0.35A. It does not have to be specifically an LED driver.

Other than from the original manufacturer, you probably won't get one with the same 24V output socket. You might have put a barrel jack socket onto the captive output lead of the new PSU, or cut the plug off the lamp cable and splice together. Beware those clear leads don't always have separate insulation for the two cores because they are designed to be moulded into the plugs.

FWIW plugs and plug-in power supplies should not be sold in the UK without either UK plug pins or a permanently attached UK converter. A separate 'travel adaptor' is not acceptable although a lot of sellers seem to think it is.
 
As it states on the unit 'constant voltage' it should be possible to replace it with any constant-voltage 24V power supply unit rated for at least 8.4W or 0.35A. It does not have to be specifically an LED driver.

Other than from the original manufacturer, you probably won't get one with the same 24V output socket. You might have put a barrel jack socket onto the captive output lead of the new PSU, or cut the plug off the lamp cable and splice together. Beware those clear leads don't always have separate insulation for the two cores because they are designed to be moulded into the plugs.

FWIW plugs and plug-in power supplies should not be sold in the UK without either UK plug pins or a permanently attached UK converter. A separate 'travel adaptor' is not acceptable although a lot of sellers seem to think it is.
Thanks for the advice. Not a simple solution then. Was hoping I could just buy a UK plug version that would fit the existing lead connection
 
You might well find a 24VDC power supply with that size barrel plug already fitted.

Also consider using one of those switchable 'universal's voltage adaptors which have an assortment of output plugs which can be fitted. Make sure it goes up to 24V though and is at least 350mA.
 
It looks like the lamp has a plug and the PSU has a socket, which is gping to be harder. I would check with the original manufacturer first.
 
It looks like the lamp has a plug and the PSU has a socket, which is gping to be harder. I would check with the original manufacturer first.

Good point. I should have read your earlier post better!!

You can get barrel connectors which join 2 DC plugs together. But as always there are issues around getting the right internal and external diameters right. I hate barrel connectors.
 
Last edited:

Reply to 24V LED Driver in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
591
Hello, Does anyone know of a Driver for led tape that can adjust the brightness on the driver itself by turning a screw etc ? Just need...
Replies
12
Views
606
Hi everyone I’m after some advice please. I’m installing some LED profile around a customers bedroom ceiling for some led strip to sit in and...
Replies
2
Views
538
Hello all. Just a bit unsure about polarity on the primary side of this LED driver. 99% certain one relates to live and two to neutral?
Replies
23
Views
2K
I’m building a vacuum exposure unit…..and so I’m sourcing a 24v transformer to match load of 24v timer…….timer will control qty 10 x 18 watt...
Replies
2
Views
463

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock