Discuss 25 year old boiler wiring in the Central Heating Systems area at ElectriciansForums.net

Andy5678

-
Esteemed
Arms
Reaction score
231
Been looking at changing a faulty timer on an oil boiler.

the current timer switches between DHW or DHW and HTG.

I cannot find any motorised valves, it looks like it’s just controlled with a room stat connected to a pump for heating and some other stat I can’t find for the water.

had a look on google and can’t find any diagrams that would suit this and the model of programmer that’s installed just now is not available.

anyone had a similar problem?
 
Sounds like a gravity fed heating system, comprising a 2 channel programmer, pump,room stat and a hot water cylinder stat. Most 2 channel programmers are capable of this but there is normally a small dip switch on the back of the programmer which needs setting to gravity fed system

EBAA4BD4-9A94-4099-9C66-6BCFAE9A2000.png
[automerge]1576784766[/automerge]
From memory these are referred to as hot water priority systems
 
Cheers, that looks like the one I need. I have just got no idea where the cylinder stat is... will go back and hunt a bit more.

the pump was down stairs under the shoe cupboard the boiler further along in utility room and the hot water cylinder upstairs with no sign of cylinder stat.

I have the dip switch setting on the new programmer.
 
Is the oil boiler in an outhouse, if so the other stat could be a frost stat.?

And it could be wired the traditional;
Hot water demand from programmer = Boiler only on (hot water temp is whatever the boiler is set to)
Heating (and hot water) demand from programmer via room stat = Boiler and pump on.

No Motorised valves used.
 
Are you sure there is a second stat? When I moved into the house I'm in many years ago all that regulated the water and house temperature was the temp setting on the back boiler (Baxi). I soon fitted a tank stat and room stat. The previous owners said it was always lovely and hot in winter. I hate to think what the gas bills were like. I currently use a Drayon LP522 timer. It's got the DIP switch on the reverse for gravity feed systems.
 
Sounds like a gravity fed heating system, comprising a 2 channel programmer, pump,room stat and a hot water cylinder stat. Most 2 channel programmers are capable of this but there is normally a small dip switch on the back of the programmer which needs setting to gravity fed system

View attachment 54743
[automerge]1576784766[/automerge]
From memory these are referred to as hot water priority systems

A gravity system does not use a cylinder stat and it is not a hot water priority system.

The programmer DHW channel directly fires the boiler, the CH channel feeds the room stat which feeds the pump.
 
I think it is a frost stat as I tested continuity across it and it was open circuit. When cold this would close and switch on heating. makes sense when following wiring on site
 
C-Plan_old2.jpgThe old C Plan relies on the time controller energising DHW at the same time as CH you can see there is no connection from room stat to boiler, it only runs pump.
With controllers where you have access to the com in the contacts and it is not fixed to the line then another possibility.C-Plan_basic_Nest.jpgNote with this the com goes to boiler, a modified form of this is what my home has, modified as the granny flat and house uses same boiler. The DHW is always running when the CH is running and the only control of the DHW is time.
 
Another possibility is to fit a 28mm 2 port zone valve to the hot water circuit, controlled by a cylinder stat. The boiler is then wired through the changeover microswitch to operate with both ch and hw controls, giving full temperature control.

Used to do a lot of these in the 80's.
 
got it going using the gravity fed option. Using frost stat, room stat and pump all wired from the programmer.

the frost stat was on the outside wall in a box!
 
Glad to see it is running @Andy5678 as to @Timbo yes I also did fit motorised valves and thermostats to gas boilers in the 80's and 90's, however was warned not to do it with oil, I am an electrician not a heating and ventilating engineer, and I really don't know in real terms if there is any extra strain on the boiler if the water is stopped from circulating, however I would if I could get a three core and earth from boiler to airing cupboard fit a thermostat for summer use. At moment in summer simple timed at 1/2 hour every other day, would be better with thermostat.
 
it’s been ok like this for many years. It’s an old couple in the house, so not wanting to do any more work that’s not urgently needing done.

In ideal world I’d be getting zone valves fitted with cylinder stat.

thanks for everyone’s input, has been very helpful
 

Reply to 25 year old boiler wiring in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
952
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
558
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
619
A nice easy one for all the (many) people that are cleverer than me 🙂. Could you please point me in the direction of a wiring diagram for a...
Replies
1
Views
915

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock