Hi folks. Just like to pick your brains for a minute. The other day I had to fit a 63a 30ma (50a mcb) shower unit for a customer having a new shower fitted who didnt want a new consumer unit (old wylex board). Split the tails with a henley block but what a job connecting them in the unit. They had to be 25mm because the service fuse was 100a but it was a real nightmare and Im sure there must be an easier way so i was wondering if any of you guys had had a similar problem and what was your solution.Ive got a few more jobs like this coming up so any suggestions would be appreciated. Many thanks ..Jon
 
Your tails can be 10mm as the 50A mcb limits the current that can be drawn through them, this would be ok only if your little shower board is one way and cant be added to for another circuit.
 
I use 10mm tails most of the time, however, 25 will fit if you bring them through the top but try and shape them before you push them through the enclosure.
 

Reply to 25mm tails to big for Shower unit ? in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
856
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock