Discuss 2way switiching- into intermediate in the UK Electrical Forum area at ElectriciansForums.net

J.C.E

-
Arms
Reaction score
158
Evening Evening!
currently have a situation where I have:

switch on loft landing (2way)
switch on 1st floor landing (2way)
which turn some down lights on/off on 1st floor

-SL from the lights is at switch on 1st floor........and 3core from here to loft lanidng

now customer ALSO wants a 3rd switch added further along in the 1st floor landing.

So I know I can change my current 2way switch on 1st floor to an intermediate switch- and run a new 3core from here to the 3rd switch (2way)


my question being- does it matter that my SL+LIVE will be at the intermediate switch- rather than one of the 2way switches (like shown in the diagram below)

-if not is it just an case of the SL and LIVE just going in L2 AND L2 of intermediate?

three_way_switching.jpg
 
Evening Evening!
currently have a situation where I have:

switch on loft landing (2way)
switch on 1st floor landing (2way)
which turn some down lights on/off on 1st floor

-SL from the lights is at switch on 1st floor........and 3core from here to loft lanidng

now customer ALSO wants a 3rd switch added further along in the 1st floor landing.

So I know I can change my current 2way switch on 1st floor to an intermediate switch- and run a new 3core from here to the 3rd switch (2way)


my question being- does it matter that my SL+LIVE will be at the intermediate switch- rather than one of the 2way switches (like shown in the diagram below)

-if not is it just an case of the SL and LIVE just going in L2 AND L2 of intermediate?

View attachment 34287
Live and switched live to Lamp? where is the the N coming from?
 

Reply to 2way switiching- into intermediate in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
589
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
608
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
600
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
530

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock