2 are in the board and the other is feeding that which is also being fed from a 100 amp rcd. cant seem to find any problems with cables and does just nuisance trip.

help plz
 
will need some more info as its a bit sparse what are the miliamp ratings of the RCD are they time delayed and what installation methods have been used for the cabling that the RCD's are supplying
 
Still need some further info.

Nuisance tripping what is tripping?

Is the 100 mA RCD a S or time delayed as if it is not you will possibly have no discrimanation !
 
yer a lil confused as to what your discribing,, as others say a lil more info is needed. and im sure someone here can help
 
whats the layout of the board and circuits, sounds like a bad setup with disgrimanation between RCDS, can you discribe the layout more or poss pics?

edit,, sounds like you also may have a fault that needs to be found as well
 
So what you are saying is you have 100 amp RCD feeding 2 63 amp RCD's or you have 100 Amp RCD feeding a dual RCD board ,if this is the case what earthing arrangement do you have , what installation methods is the 100 amp RCD suppling the 63 amp RCD's answers to these questions will help us give you the answer you are looking for sorry to be a pain but the more info you give the better the advice
 
whats the layout of the board and circuits, sounds like a bad setup with disgrimanation between RCDS, can you discribe the layout more or poss pics?

edit,, sounds like you also may have a fault that needs to be found as well

100 amp feeding a 63 amp under board the feeding a dual Rcd board.
 
100 amp feeding a 63 amp under board the feeding a dual Rcd board.

hmm as others keep saying, im a lil lost as well.. your saying 100 amp feeding 63 amp and then a duel rcd board? are you meaning to say... A 100amp 30ma RCD feeds a 63amp 30ma RCD then goes off to a duel 30ma RCD board? If you are then the whole install is inaproprate and needs looking into, we will then need to know more about the setup to see if any distribution circuits can come off RCDs to stop the problem...
also to dig deaper, is it a TT system?
 
Last edited by a moderator:
hmm as others keep saying, im a lil lost as well.. your saying 100 amp feeding 63 amp and then a duel rcd board? are you meaning to say... A 100amp 30ma RCD feeds a 63amp 30ma RCD then goes off to a duel 30ma RCD board? If you are then the whole install is inaproprate and needs looking into, we will then need to know more about the setup to see if any distribution can come off RCDs to stop the problem...
also to dig deaper, is it a TT system?

yes that's exactly what I'm saying. I'm not sure if it's tt it's a possibility !
 
So 100 amp RCD feeding a 63amp RCD feeding a dual RCD board , or is it 100 ma RCD feeding a 63 amp RCD feeding a dual RCD board is the install TNCS , TT ,or TNS
 
TNCS where the earth is linked to neutral often internally with a block off the side of the cut out , TT uses and earth rod ,TNS where the outer sheath is used as the earth If its a TT supply then you will only need the dual RCD board unless its metal clad where you will need a 100 ma or 30 ma time delayed RCD we could do with a picture so we can offer the correct information
 
2 are in the board and the other is feeding that which is also being fed from a 100 amp rcd. cant seem to find any problems with cables and does just nuisance trip.

help plz

how long has this been setup like this? is it a new install? the setup seems a bit problematic and not thought through.. if its an old install i would be getting th IR tester out... if new i would be getting the install sparks out!
 
It's defo not 100 ma. It's 100 amp. It is the main switch to a 3phase board and one phase goes below to a 63 amp with 45 amp breaker like a mini board . The that goes to a dual Rcd board
 
how long has this been setup like this? is it a new install? the setup seems a bit problematic and not thought through.. if its an old install i would be getting th IR tester out... if new i would be getting the install sparks out!

ot it could have been installed by a spark with a fear of electric shock..
 
how long has this been setup like this? is it a new install? the setup seems a bit problematic and not thought through.. if its an old install i would be getting th IR tester out... if new i would be getting the install sparks out!
It's new . Last year . Yeah seems they have messed it up. It's been like this awhile but the install has never been used properly just now and then
 
thought I had the install setup in my head,, but im missing things?? 100amp 3 phase main swith with no RCD that sound normal? to a 63amp with 30ma rcd? which is where? off to a duel board... sorry im not getting it now.. dont get frustrated kay, but a few pics may really help here as your termnoligy seems a lil off m8,, in the politest manour..

ps my spelling seems to suck
 
thought I had the install setup in my head,, b ut im missing things?? 100amp 3 phase main swith with no RCD that sound normal? to a 63amp with 30ma rcd? which is where? off to a duel board... sorry im not getting it now.. dont get frustrated kay, but a few pics may really help here as your termnoligy seems a lil off m8,, in the politest manour..

ps my spelling seems to suck

can't seem to upload pics.

100 amp is Rcd mate. To a 63 Rcd below board and then off to a dual Rcd.
 
2 pages of compressed descriptions of the install and questions on that set up in each post,my eyes ache
icon10.png
 
so we got a 100amp 30ma rcd at the front end (3 phase)( thats a pain in the butt too start with),, if this is so then get rid of the others, their not needed.....wonders why they were fitted.. if its not tt then get rid of the front end rcd and use rcbos for the circuits that req rcd.... sorry if im not more helpfull...
 
so we got a 100amp 30ma rcd at the f ront end (3 phase)( thats a pain in the butt too start with),, if this is so then get rid of the others, their not needed.....wonders why they were fitted.. if its not tt then get rid of the front end rcd and use rcbos for the circuits that req rcd.... sorry if im not more helpfull...

ok that's what I was thinking . I can take the rcds out and just use the main switch as isolation in dual board
 
sorry went to bed!,, If its TT then the RCDs are required, but not all of them I would be looking at trying to remove the 3 phase RCD and fit a main switch then fit rcbo's to final circuits that are fed from the 3 phase board, and an MCB to feed the other RCD protected board..hopefully there aint many ways on the 3 phase board. at least this spreads the loads and any faults will trip the approprate RCD.
 
Last edited by a moderator:
sorry went to bed!,, If its TT then the RCDs ar e required, but not all of them I would be looking at trying to remove the 3 phase RCD and fit a main switch then fit rcbo's to final circuits that are fed from the 3 phase board, and an MCB to feed the other RCD protected board..hopefully there aint many ways on the 3 phase board. at least this spreads the loads and any faults will trip the approprate RCD.

okay I've changed a few things around today ... I've taken out the Rcd below board . I've notices as well it seems to trip when it gets a surge of current ie printer or hand dryer. The 3phase braker is an old mem one so could be a problem changing that
 
Do you have an IR tester? as what you are discribing could well be an underlying low resistance that on its own is not enougth to cause a tripping situation, but when a suden increase in load is seen it unbalences the RCD. (this is very common)
 
Do you have an IR tester? as what you are discribing could well be an underlying low resistance that on its own is not enougth to cause a tripping situation, but when a suden increase in load is seen it unbalences the RCD. (this is very common)

I have s fluke multimeter yeah . What's the best way of sorting it ? Remove Rcd?
 
I know your right but the customer has also ask me to do this . I have not no

If faced with a fault on a circuit where the CU has rewireable fuses and the the customer asks you to replace the fuse wire with a nail would you do it?
If the fault is on the circuit then the RCD's only doing its job.You'd be removing the protection not the problem
Is it a multimeter or a multifunction tester you have?
The best way for these guys to help you out would be to post some pictures and give as much info as possible,what tests you've carried out and the results
 
sry King11 but without an IR (insulation resistance) tester finding the underlying fault is gona be almost imposible, and time consuming, at best your gona be guessing.. And as the others have said dont remove the RCD just because the cliant has asked, it WILL be your arse on the line.
 
sry King11 but without an IR (insulation resistance) tester finding the underlying fault is gona be almost imposible, and time consuming, at best your gona be guessing.. And as the others have said dont remove the RCD just because the cliant has asked, it WILL be your arse on the line.

I noted my comment about IR tested went unanswered.... may be it will now.
 
What you don't want is the next call being to the fire service once the RCD is removed!

I wonder who the client would blame when they insist they know nothing about electrics and RCD's stating that why they contacted a electrician!

A RCD trips for a reason and that need to be established or walk away from the job IMO!
 
SO many unanswered questions on this, or questions that need to be asked. Have you considered getting another sparks in to do this one on your behalf? You sound a little out of your depth.
 
okay think ive found the faulty circuit, i did IR and got 223 on E - N and L - N }500 set on 500v. its a light cicriut 1.5mm

223 & 500 what Ω or MΩ

I think you need to consider involving some one with a little more knowledge than yourself in the best interests of all concerned
 
Sounds like a non sensicle installation. 100A RCD feeding 63A RCD all 30mA instant... Why? you have discrimination issue immediately. The second MCB seems to serve no purpose - could just be a MCB.
 
200 odd MOhms is a perfectly acceptable value, so not sure how you can claim that to be the fault when clearly so many other issues seem to exist. Do the maths, and you'll see why it's not going to be an IR value of 200M that's causing a 30mA RCD to trip.
 
Do you have an IR tester? as what you are discribing could well be an underlying low resistance that on its own is not enougth to cause a tripping situation, but when a suden increase in load is seen it unbalences the RCD. (this is very common)


Correct! You know your stuff mate! #cheers

 

Reply to 3 63 amp RCDs on same circiut in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
397
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
989
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top