Still need some further info.
Nuisance tripping what is tripping?
Is the 100 mA RCD a S or time delayed as if it is not you will possibly have no discrimanation !
whats the layout of the board and circuits, sounds like a bad setup with disgrimanation between RCDS, can you discribe the layout more or poss pics?
edit,, sounds like you also may have a fault that needs to be found as well
100 amp feeding a 63 amp under board the feeding a dual Rcd board.
hmm as others keep saying, im a lil lost as well.. your saying 100 amp feeding 63 amp and then a duel rcd board? are you meaning to say... A 100amp 30ma RCD feeds a 63amp 30ma RCD then goes off to a duel 30ma RCD board? If you are then the whole install is inaproprate and needs looking into, we will then need to know more about the setup to see if any distribution can come off RCDs to stop the problem...
also to dig deaper, is it a TT system?
2 are in the board and the other is feeding that which is also being fed from a 100 amp rcd. cant seem to find any problems with cables and does just nuisance trip.
help plz
how long has this been setup like this? is it a new install? the setup seems a bit problematic and not thought through.. if its an old install i would be getting th IR tester out... if new i would be getting the install sparks out!
It's new . Last year . Yeah seems they have messed it up. It's been like this awhile but the install has never been used properly just now and thenhow long has this been setup like this? is it a new install? the setup seems a bit problematic and not thought through.. if its an old install i would be getting th IR tester out... if new i would be getting the install sparks out!
thought I had the install setup in my head,, b ut im missing things?? 100amp 3 phase main swith with no RCD that sound normal? to a 63amp with 30ma rcd? which is where? off to a duel board... sorry im not getting it now.. dont get frustrated kay, but a few pics may really help here as your termnoligy seems a lil off m8,, in the politest manour..
ps my spelling seems to suck
I think the only way forward would be a couple of pictures ... and what test equipment do you have at your disposal?
Fluke multimeter
so we got a 100amp 30ma rcd at the f ront end (3 phase)( thats a pain in the butt too start with),, if this is so then get rid of the others, their not needed.....wonders why they were fitted.. if its not tt then get rid of the front end rcd and use rcbos for the circuits that req rcd.... sorry if im not more helpfull...
sorry went to bed!,, If its TT then the RCDs ar e required, but not all of them I would be looking at trying to remove the 3 phase RCD and fit a main switch then fit rcbo's to final circuits that are fed from the 3 phase board, and an MCB to feed the other RCD protected board..hopefully there aint many ways on the 3 phase board. at least this spreads the loads and any faults will trip the approprate RCD.
I've notices as well it seems to trip when it gets a surge of current ie printer
Do you have an IR tester? as what you are discribing could well be an underlying low resistance that on its own is not enougth to cause a tripping situation, but when a suden increase in load is seen it unbalences the RCD. (this is very common)
I have s fluke multimeter yeah . What's the best way of sorting it ? Remove Rcd?
Removing the RCD may cure the "pain" for the client but is not the way to fin d andfix the fault. Have you IR'ed anything?
I know your right but the customer has also ask me to do this . I have not no
sry King11 but without an IR (insulation resistance) tester finding the underlying fault is gona be almost imposible, and time consuming, at best your gona be guessing.. And as the others have said dont remove the RCD just because the cliant has asked, it WILL be your arse on the line.
i know it wouldnt leave the install like it permentaly they really need to use the install so it would only be temp if i did
okay think ive found the faulty circuit, i did IR and got 223 on E - N and L - N }500 set on 500v. its a light cicriut 1.5mm
Do you have an IR tester? as what you are discribing could well be an underlying low resistance that on its own is not enougth to cause a tripping situation, but when a suden increase in load is seen it unbalences the RCD. (this is very common)