dlt27
-
- Reaction score
- 26
The company I work for sent out some guys to connect up some temps through a 3 phase meter. Now the circuit was fed via an existing board with a 63A breaker and the existing board was backed up by a 160 amp mccb.(plus an rcd for the sub-main). The 3 phase meter so I have been told went up in smoke on 2 occasions and took out both breakers.
On the 3rd occasion I was sent to check it out. I found 2 phases reversed at db ie brown and grey connected wrong way around and I found brown phase to be carrying 96A and other 2 phases about 35A . I put everything right with phases and balanced loads so all were carrying about 50A. (Also existing meters were direct connect.) All I wanted to know is if anyone knew which of these faults would cause the meters to burn out?
I thought if phases were reversed it would just cause the wheel to clock backwards and also thought meters would carry 100A fine. Thanks for any info.
On the 3rd occasion I was sent to check it out. I found 2 phases reversed at db ie brown and grey connected wrong way around and I found brown phase to be carrying 96A and other 2 phases about 35A . I put everything right with phases and balanced loads so all were carrying about 50A. (Also existing meters were direct connect.) All I wanted to know is if anyone knew which of these faults would cause the meters to burn out?
I thought if phases were reversed it would just cause the wheel to clock backwards and also thought meters would carry 100A fine. Thanks for any info.