Discuss 3 phase meter in the Electrical Forum Canada area at ElectriciansForums.net

dlt27

-
Reaction score
26
The company I work for sent out some guys to connect up some temps through a 3 phase meter. Now the circuit was fed via an existing board with a 63A breaker and the existing board was backed up by a 160 amp mccb.(plus an rcd for the sub-main). The 3 phase meter so I have been told went up in smoke on 2 occasions and took out both breakers.
On the 3rd occasion I was sent to check it out. I found 2 phases reversed at db ie brown and grey connected wrong way around and I found brown phase to be carrying 96A and other 2 phases about 35A . I put everything right with phases and balanced loads so all were carrying about 50A. (Also existing meters were direct connect.) All I wanted to know is if anyone knew which of these faults would cause the meters to burn out?
I thought if phases were reversed it would just cause the wheel to clock backwards and also thought meters would carry 100A fine. Thanks for any info.
 
I've never seen a metering unit that could be damaged by phase reversal. A make and model number for the meter would help so we can look for an on-line datasheet.

I assume this was direct on-line metering, not CT metering. Most likely terminations or possibly a highly inductive or capacitive load if it's an industrial installation.
 
I’ll go along with Mavo (but not if he’s wearing that outfit, I do have standards). Reverse phases won’t make any difference. It could only be load or poor terminations. As most meters are designed to withstand a reasonable amount of overload then I’d look at the terminations.
 
Hi Gang , sorry to interject and change the subject slightly , however have been asked to fit a 3 phase meter in an industrial / commercial unit . The meter is going to be situated adjacent to the tennants DB so they know the landlord is not ripping them off . My question is , do i need to fuse the CT's if so i have read that the fuse must go before the CT , how is this possible if we are unable to remove the incomers from the dB due to their work load in unit . I know i can use split CT's but just wondering about the fuses
 
You should start a new thread not resurrect an old one. This was dead and buried.

You can get shell type CT’s (in two halves). BUT do not fit them with the board on load! (Unless you’ve got a death wish). Select your time, lunch break, shift changes or night time.
 

Reply to 3 phase meter in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
658
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
1K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
978
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock