Discuss 3-Phase Motor Testing in the Industrial Electricians' Talk area at ElectriciansForums.net

D

Darrensparky

Hi I'm Darren and I work as a apprentice for a manufacturing company.

I was testing a 3kw 3-phase motor as it blew a fuse and when doing my IR test down to earth I got a reading of around 11Gohms. I was under the impression that the reading had to be above 1Mohm which this is as far as I am aware but I was advised by my colleague that this is a bad reading and the motor is no good. Can someone confirm for me if I am right or wrong and why :)


Thanks
 
that is an extremely high reading. as 1 Gig is 1000 Meg. most IR testers won't read that high. if it blew a fuse, i'd be inclined to IR measure between each winding and also a resistance test of each winding. if good, then fire it up with new fuse and measure currents.
 
As tel said, you have you ohms mixed up somehow.

Test all phases to ground again and between them @500v. Then check all the windings are balanced (the same).

Does the motor run freely?
Clamp on your ammeter and see what the FLC is.
 
I usually take a hammer to the blown fuse and post mortem it to see if it went with a proper bang or whether it was just a lazy blow.

11Gohms is an enormously high IR reading, not sure why your colleague would be unhappy with it......
 

Reply to 3-Phase Motor Testing in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
340
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
657
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock