Discuss 3 phase motor wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
Hi just after some advice on how to wire this water motor. I have follwed the wiring diagram, when I test it, just get a buzz from the motor, Not spinning at all. Tried switching line conductors, same result.

Supply is 3 phase & Neutral.

Thanks

95ECE7CE-85C7-4EBB-9AA6-750D4ACA24A0.jpeg


D8195041-AC40-4940-9A55-43ED07376E9B.jpeg


965069FF-9810-4821-BBAE-9393E4879765.jpeg


5C3C7797-E41E-454F-83D8-388D3E381B06.jpeg


68154103-2BE6-46CA-8AF6-FD97F049E548.jpeg
 
diss. the control circuit cables. then try pressing the contactor in manually. if it fires up then, you have a control circuit fault/incorrect wiring/incorrect coil volts.
 
When a motor won't run, always worth checking that all phases are present i.e. 400V between them and 230V to N or E, before anything else. Would have picked up the starter wiring error instantly. If all OK, then usually it's a miswire of the motor leadouts.
 
You may have already damaged the motor windings by running it on 2 phases, disconnect the cable and test the motor windings for continuity resistance and IR @ 500v.

What is the rated run current on the motor info plate? 9 Amps setting on the thermal overload looks high for that motor but sometimes photos are decieving.
 
Sounds like a suck it and see scenario, to me.
Messing about with 3 phase motor supply and control can be very dangerous without the necessary experience.
If you're qualified, you're misreading a very basic situation.
If not, you shouldn't be touching this.
 

Reply to 3 phase motor wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
336
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
798
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
634
hi Can anyone tell me where to wire the active and neutral wires to in this single phase electric motor
Replies
1
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock