Hi all
In order to measure your pefc pscc, you need to test across all 3 line conductors then multiply by 2 record the highest value, this is correct isnt it.
 
Hi all
In order to measure your pefc pscc, you need to test across all 3 line conductors then multiply by 2 record the highest value, this is correct isnt it.

The PSCC will be the highest in a three phase installation. Double the highest line to neutral value if your equipment cannot measure between phases.
 
Hi all
In order to measure your pefc pscc, you need to test across all 3 line conductors then multiply by 2 record the highest value, this is correct isnt it.

Each line conductor separately the same method and connections as if you were doing it on single phase, take the highest of the 3 readings, and as you say double it. Job done.
 
Actually, I read that the reason for the x 2 is to allow for the remote possibility of a fault across all three phases, which is closer to 2x PFC of one phase to N or E, than 1.732 x
if I remember correctly it was Geoff Cronshaw on the IET forum. I may be mistaken, but I'm sure I'm not.
 
Actually, I read that the reason for the x 2 is to allow for the remote possibility of a fault across all three phases, which is closer to 2x PFC of one phase to N or E, than 1.732 x
if I remember correctly it was Geoff Cronshaw on the IET forum. I may be mistaken, but I'm sure I'm not.

whats 0.268 between friends ? ;-)
its enough to blow your face off whatever the final figure lol.
 
and Riz being the french for rice and La+ originating from Lacroix.
thought you were going to challenge me there.
archy caught with pants down ;-)

i'm too fast old man. :-D
 

Reply to 3 phase pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
929
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
411
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top