Allan, my course tutor, has just told me that (in his opinion) if the plate on a 3 phase motor says (eg) 10kW, that's the total consumption.

Do us a cheeky favour tell your tutor the KW rating on a motor is the energy output down the shaft and a replacement value for horsepower and not to be confused with what the motor consumes thus the relevant equation has to be done to get the current before you can say whether its across the phases or per phase - Im interested ho you are taught today and what his answer would be!
 
There are also still some glaring errors in posts on this thread ignoring the so called "misunderstanding" of kW per phase or across 3 phases that are sufficient to kill people.

Yes there are but it's a discussion, not a tutorial and if anything should be taken from the thread by a person looking for advice it should be that they ought to confirm with the agents or supplier before making any assumptions.
 
Do us a cheeky favour tell your tutor the KW rating on a motor is the energy output down the shaft and a replacement value for horsepower and not to be confused with what the motor consumes thus the relevant equation has to be done to get the current before you can say whether its across the phases or per phase - Im interested ho you are taught today and what his answer would be!

To be fair to Allan, he did say rather a lot more than the sentence I typed quickly on my phone during the brew break! I realise now that in my rush, I probably misrepresented what he explained. Apologies.

Over 3-4 minuts he talked about how (as you say) it's related to the output power of the motor in terms of the work it can do. He mentioned horsepower, and when he put it in this perspective it started to make sense. He did mention efficiency too; he didn't actually say, "Your total electrical power consumption will be greater than the rated power due to the efficiency always being less than one (100%)," but we covered the equations in an earlier lesson so I guess he left this for us to work out.

I like Allan. He's alright.
 
@NickD

I'll apologise now for taking this off topic (as I know it's now frowned upon)

Nick do you find Asperger's is much of a hindrance to how you deal with your life on a day to day basis?
My great nephew has it and it's a daily struggle for him.

I reckon he had his Bell End pulled and he's replaced it with this lame attempt.
 

Reply to 3 phase supply size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
wiring a 480 volt 3 phase 114 amp generator to run 2 machines. Both machine nameplate 480 v 3 phase 50 FLA. What size wire and over current...
Replies
0
Views
962
Hi, we are converting old farm buildings to commercial units, and as my father used to run a vacuum pump and compressor in his dairy I always...
Replies
13
Views
2K
Hi all, I have been asked to install individual three-phase supplies for a band saw and table saw. Having trouble figuring out the correct cable...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock