Discuss 3 Phase welder in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Currently looking at a job to install power for welders. I asked for the size of the welders and customer has replied with MIG 32A 3Ph = 14KVA.
So i can work out total loadings for the installation have a i done the following sum correctly?

14kva X PF of 0.8 = 11.2kw

A= 11.2 x 1000/415 x 1.732 x PFat 0.8

I get 37.39A so 12.46 A per phase?
 
you're out, IMO. i get 24.5A (19.5 @ unity pf)
 
Last edited:
14000/ (1.732 x 415 x 0.8)

14000/575

24.348A
 
OP was using a pf of 0.8. not sure if that's on the equipment spec. though.
 
415 x 1.732 old money converts the result to 1 phase

You got the wrong result to start with ... (see post 6 for the correct method)... disregarding thewrong result you then divided it by 3 to try get a per phase result... so you attempted to get from 415 to 240 twice as well as doing PF twice.
 
415 x 1.732 old money converts the result to 1 phase

You got the wrong result to start with ... (see post 6 for the correct method)... disregarding thewrong result you then divided it by 3 to try get a per phase result... so you attempted to get from 415 to 240 twice as well as doing PF twice.

KVA is the total current drawn, so 14000/692 is the correct answer.

Cheers
 
It helps if you apply PF correctly.

Weldingset_zps55df00e3.jpg
 
It helps if you apply PF correctly.

Weldingset_zps55df00e3.jpg

It does, and when you have a KVA value its been adjusted. PF is just the ratio of KW/KVA.

Now S= KVA, P=Watts and Q=Var

Now KVA is the product of true and reactive power, KVA is apparent.

So we Know KVA(S) = 14, so to find our KW(P) its 14 X 0.8 = 11.2 KW.

To find KVar we need a bit of trig and we find Kvar = 8.4.

So we have all three sides to our power tringle.

S= 14kVA
P=11.2kW
Q=8.4kVAR

So the total current drawn by the welder is S, so 14000/692 is the correct answer.

Cheers
 
If you go back to the original question “what is the current loading?”

Your answer gives the current for unity PF which isn’t what was asked for. Any protection will have to account for the increase caused by 0.8PF. IE kW x the inverse PF

This develops in to an interesting situation on large motors where local PFC is installed. The O/L settings have to be lower than the motor manufacturers rating plate. RoB2 has written an excellent article about this elsewhere.
 
If you go back to the original question “what is the current loading?”

Your answer gives the current for unity PF which isn’t what was asked for. Any protection will have to account for the increase caused by 0.8PF. IE kW x the inverse PF

This develops in to an interesting situation on large motors where local PFC is installed. The O/L settings have to be lower than the motor manufacturers rating plate. RoB2 has written an excellent article about this elsewhere.

Not what I would call it, nothing but a pain in the ---!
 

Reply to 3 Phase welder in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an old Migatronic Automig X 200 welder configured as 380V 3-phase unit. Migatronic for spec. I have a 220V 3-phase point in my garage...
Replies
4
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
998
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock