ezzy99

Howdy,

Moved into our house over a year ago and have only just found out we have a problem with the hall lights. There are 3 single switches in the hall that run a ceiling full of spots. The problem is that occasionally I turn on one of the switches (can be any of the three) and the lights do not change. If they are on and the switch is pressed they stay on and vise verser. Its starting to frustrate me now as it seems to be when I come home from work in the night and turn the switch at the front door on it doesnt work. When I come in from the garage and use the switch at the back of the door that doesnt work. It seems to follow me about the very switch i want to use doesnt work so i need to randomly press the 3 switches to get them to work!!!!!!!! Please help!!!


Cheers
ezzy99
 
Maybe connected up wrong at the back....or there may be damaged insulation on the conductors and its shorting across.....switch wire to switch wire as its bound to be quite congested behind that 3 gang switch plate.........
 
could be that conductors are finding a way across via the metal backbox if the insulation is damaged......what kind of fuse board do you have....rewireables? RCDs?....RCBOs?
 
You have 2 No 2 way switches and 1 No intermediate
You probably have mixed up connections in one or other or even all of them

This was a thread on the subject ,there are many more
http://www.electriciansforums.net/e...rum/42324-two-way-intermediate-switching.html


Look at the wiring diagrams and compare to yours and alter to suit
You may need a spark if you cant understand the layout
I didn`t read the first post properly des...I agree with you it sounds like mixed up wireing.......
 
I didn`t read the first post properly des...I agree with you it sounds like mixed up wireing.......

I suspected that was the case Glen,being a sadistic b-----d I just let you carry on
icon7.png
 
I fixed an issue alongs these lines a while back. Customer had changed the switches and had got the cores/cables mixed up. Took a little while with my tester and wander lead to get it sorted.
 
If nothing has changed then the problem is likely to be broken insulation or, as you are switching a lot of downlights, you may be getting one of the switches welding itself closed with the current and would require a new switch at the appropriate position.
If things have changed then the wiring should be checked, safely with the power off and a tester.
I attach a picture of the standard wiring diagrams for lighting taken from the TLC website for reference.
View attachment lighting WiringDiagrams.pdf
 
Thanks guys for your replys (Glennspark, Des56) wasnt going to look back on here tonight was going to give it a couple of days. What a great forum. Literally only got in from work so to dark to look into things tonight but I plan to investigate further. Not sure how I post pictures on here yet but Ill probably post a few tomorrow showing the back of the swithces. Again thanks for your replys.
 
Thanks for the reply (murdoch, richard burns). Just got back from work so to dark to really investigate plan to have a look at the back of switches and possibly take photos to post. Cheers
 
Last edited by a moderator:
comedian??? i ain't started yet. LOL. joking apart, some pics would help. isolate at the Consumer Unit before taking faceplates off, and please, don't disconnect any wires. that could make the situation 10 times worse.
 

Reply to 3 switches 1 light problem! in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
626
Suggestions / solutions please anyone? I have a 2 way switch, Hall and Landing, power being fed on Landing. When the switch is turned on, the...
Replies
2
Views
525
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
853
I fitted an Ener-J wireless receiver and switch from CEF. During course of afternoon one light fitting kept turning on and off unexpectedly but it...
Replies
5
Views
615
I can't seem to find the right answer for a smart switch installation for a light that has THREE switches. There's conflicting information, and...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock