I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

IMG_5741.JPG


Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

IMG_5742.JPG


Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
 
Seems like a lot of work for a problem that doesn't / shouldn't exist.

The only time I've had that issue is when refitting very cheap sockets where there isn't really enough space for the 3 wires or they have been cut too short and my fat paws won't fit.
 
It does mean less risk of things being disturbed when the socket is wraggled on to the back box. And the stranded singles will make things easier. As above though, quite a bit off faffing.

Be interesting to see what people think.
 
Aren't you technically taking two spurs from one point of the ring though?

IE you have ring in and out, plus the third to your spur - but then the socket its behind is also a spur - as the point of junction is now the wagos rather than the socket faceplate
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Why not just use the

MK LOGIC RAPID FIX

 
Aren't you technically taking two spurs from one point of the ring though?

IE you have ring in and out, plus the third to your spur - but then the socket its behind is also a spur - as the point of junction is now the wagos rather than the socket faceplate
I agree, he's turned the existing socket into a spur.
 
Effectively picture #2 is what they do in America / Canada called PIG TAILING , they do it a lot over there using Wire Nuts to bind all the cores together in the back of the box and just take a single cable to the socket or as they call it the receptacle.
Most sockets will take 3 x 2.5 cores , except for the really cheap carp ones
 
never had an issue before... not with new, clean solid core. As you tighten the terminal screw, the cores will turn so the screw is gripping two cores, and the other is pressed into the back of the hole.
Never twist together.

stand by for other manufacturers following MK..... Still not used one yet, but i can see it being a time saver if fitting out an entire house.
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Will you be going back to the jobs to correct them ?
 
I believe MK are about to start selling a level connection fused Spur and light witch range later this year
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Ridiculous in my honest opinion
 
Will you be going back to the jobs to correct them ?
Why would he go back and correct them, yes its a technical breach of the regs but there's nothing dangerous in what he's done, its still the same number of sockets in the circuit its just that the joint is in the wago and not the socket, those wagos can withstand about 100 amps before they melt according to several video's I've watched on them. I would only ever go back to a job if I realised I'd done something dangerous.

Saying that, its well over the top, those wagos are about 20p each, a pack of ferules, cable ties, 3 coils of conduit cable, might as well not bother doing the job at all. I don't get why people end up with spurs on new wiring anyway, I work with someone who always manages to do this, there is always a socket somewhere that has 3 cables at it on one of his re-wires, it cant be that hard to go in a circle can it
 
Pig tailing / splicing / the cables in the back of the box like this using Wagos really isn't an issue as long at the linking single cable is 2.5 or bigger and the OCPD is 32amps or lower.
Wagos are pretty much bomb proof and would run 30amps all day long without so much as breaking a sweat
 
Why would he go back and correct them, yes its a technical breach of the regs but there's nothing dangerous in what he's done, its still the same number of sockets in the circuit its just that the joint is in the wago and not the socket, those wagos can withstand about 100 amps before they melt according to several video's I've watched on them. I would only ever go back to a job if I realised I'd done something dangerous.

Saying that, its well over the top, those wagos are about 20p each, a pack of ferules, cable ties, 3 coils of conduit cable, might as well not bother doing the job at all. I don't get why people end up with spurs on new wiring anyway, I work with someone who always manages to do this, there is always a socket somewhere that has 3 cables at it on one of his re-wires, it cant be that hard to go in a circle can it
It was a question to the OP asking if he was going back to correct the non-compliant installation.

If you're happy to install from new, something that is non-compliant that's on you, personally I wouldn't do it because I wouldn't want anyone in the future to drop the socket and think WTF.

Doing what he did has made it less safe than joining them in the socket, he has introduced more joints and turned the original socket into a spur.
 
Last edited:
It was a question to the OP asking if he was going back to correct the non-compliant installation.

If you're happy to install from new, something that is non-compliant that's on you, personally i wouldn't do it because I wouldn't want anyone in the future to drop the socket and think WTF.
Is it actually non-compliant though?
 
It was a question to the OP asking if he was going back to correct the non-compliant installation.

If you're happy to install from new, something that is non-compliant that's on you, personally I wouldn't do it because I wouldn't want anyone in the future to drop the socket and think WTF.

Doing what he did has made it less safe than joining them in the socket, he has introduced more joints and turned the original socket into a spur.
I wouldn't do that either but if I did do something that later turned out to be a technical breach but was perfectly safe I wouldn't be going back to alter it. Especially after seeing the cowboy stuff from otheres that is churned out on a daily basis without a care in the world.
 
I would say so as it's 2 spurs from one point of a ring final.
I don't think this is prohibited by appendix 15 though is it? It's not a spur off a spur, so shouldn't be issues with the cable overloading. The wagos wouldn't be subject to any more current in this arrangement than the terminals of the socket would be if the spur was terminated into the back of the socket, if you see what I mean.
 
I don't think this is prohibited by appendix 15 though is it? It's not a spur off a spur, so shouldn't be issues with the cable overloading. The wagos wouldn't be subject to any more current in this arrangement than the terminals of the socket would be if the spur was terminated into the socket, if you see what I mean.
One spur per socket outlet is compliant, basically this is now 2.

The load of the ring and the load from two spurs is now on the Wago the socket connection IMO is far more substantial than the Wago.
 
One spur per socket outlet is compliant
I wouldn't choose to strongly say this as nothing normative in the regs states this. The normative reg tells us that the load in any part of the circuit shouldn't exceed the cable rating for long periods. So unless there are consistent loads I don't see how we can state the level of compliance for this sort of arrangement.

As a point of interest, if it had been one of these, would you still feel the same?

1688843267185.png


Surprisingly, as chunky as it looks it has a lower rating than those Wago connectors.
 
I wouldn't choose to strongly say this as nothing normative in the regs states this. The normative reg tells us that the load in any part of the circuit shouldn't exceed the cable rating for long periods. So unless there are consistent loads I don't see how we can state the level of compliance for this sort of arrangement.

As a point of interest, if it had been one of these, would you still feel the same?

View attachment 109280

Surprisingly, as chunky as it looks it has a lower rating than those Wago connectors.
Yes, I would feel the same, as I wouldn't run 2 spur sockets from one junction box.

Btw Wago 221 seem to vary in current rating, I've seen some rated at 20 amps some at 32 and some at 41.
 
Looking at the photo maybe could be dressed in a bit better on the forming of the conductors, more of a sharper bend. Not the greatest example for this situation dry lined box on stud wall but hey gotta work with it.
Metal boxes on a solid wall would be much easier I would dress all the conductors all in the same direction then sweep them back round on themselves dress them in back into the box before even trying to screw them up.
 
I don't think this is prohibited by appendix 15 though is it? It's not a spur off a spur, so shouldn't be issues with the cable overloading. The wagos wouldn't be subject to any more current in this arrangement than the terminals of the socket would be if the spur was terminated into the back of the socket, if you see what I mean.
It looks like this has already been discussed in another thread, It seemed to have caused a divide.


What has come about from this somewhat heated debate, is one or two members have either contacted their respective C.P.Schemes, the NICEIC in this instance, or the IET directly, both organisations have declared that the issue presented to them by members of the Forum, in their opinion, is non-compliant with BS7671.
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Is it just me or the photo quality but looking closely especially the L I can’t see the cable pushed fully into the wagos.
 
It looks like this has already been discussed in another thread, It seemed to have caused a divide.


What has come about from this somewhat heated debate, is one or two members have either contacted their respective C.P.Schemes, the NICEIC in this instance, or the IET directly, both organisations have declared that the issue presented to them by members of the Forum, in their opinion, is non-compliant with BS7671.
I can only really repeat what I said before. In post #1, picture2, the wago would receive the same load as the terminals of a socket would, if spurred from in the usual way (as in post #1, picture 1). The ring would receive the same load at that point wired either way. The 32A wago is protected by the 32A breaker.

The wago arrangement isn't shown in the design guide, but I see no less protection against overload, or anything else, in this arrangement. I don't think it is prohibited by regulation, and I don't think the OP should go back to alter the work.
 
If this was an old socket with cores too short to reach the new socket then I would have used Wagos connectors just like the OP and made up some 2.5mm flying leads to make off in my new socket front.
I think some people are getting their goat with he OP as the cables 'could have' just been put into the back on the socket and no need for the flying lead wago c
 
OP here: Quick update as busy this week.

I never said this was an RFC. (Although I believe it would not matter if it were, for reasons I’ll explain in detail later.)

It’s a 2.5mm radial protected by a 20A RCBO, in a commercial setting.

The third cable goes off to a distant display screen up on the wall. I considered it better engineering practice to ‘spur’ this accessory rather than go all the way up there and back again with a continuous radial, which would have made the total circuit length much longer.
 
It looks like this has already been discussed in another thread, It seemed to have caused a divide.
Yes I think I recall that one of the moderators had to step and and stop that discussion as it had gone from technical to personal insults, which is not what the forum strives for.
What has come about from this somewhat heated debate, is one or two members have either contacted their respective C.P.Schemes, the NICEIC in this instance, or the IET directly, both organisations have declared that the issue presented to them by members of the Forum, in their opinion, is non-compliant with BS7671.
Again, maybe I am thinking of another thread, but in the one that was stopped the argument was that the Wago itself was part of the RFC so you could take multiple loads off it. I think most folks (including myself) disagreed with that view and took the more reasonable approach that the Wago is no different to a terminal on an accessory so what matters is the total load on a point of the RFC not causing too much imbalance between the 'legs' which the usual diversity of fuse-limited loads spread over the overall length of the RFC would offer.

The issue with the "spur off a spur" sort of DIY is that 2.5mm cable can have its nominal 20A rating exceeded hence the prohibition on that, unless off a FCU or similar that limits the total load.

What the OP is showing is not quite the same, as basically you have a double socket and a spur connected to the same location of the RFC. I don't see this as any different to taking a spur off the double socket in the conventional case as the total load on the RFC at that point is the same, and it is not flowing through a single section of 2.5mm

EDIT: Seems it was a radial, but above still of interest to discuss!
 
Last edited:
It’s a 2.5mm radial protected by a 20A RCBO, in a commercial setting.
OK, then no issues whatsoever as none can be overloaded.
The third cable goes off to a distant display screen up on the wall. I considered it better engineering practice to ‘spur’ this accessory rather than go all the way up there and back again with a continuous radial, which would have made the total circuit length much longer.
Its a trade-off, you lose the end-socket test for continuity on all socket's CPC, etc, but gain less volt drop & cost.
 
Sorry...
It's not been a good day so far!
Off on holiday tomorrow to the land where choc-block and leccy tape rules!
...and nobody dies!
Well, not many from electrocution anyway...
 
Sorry...
It's not been a good day so far!
Off on holiday tomorrow to the land where choc-block and leccy tape rules!
...and nobody dies!
Well, not many from electrocution anyway...
Take some wire nuts with you to give 'em some more ideas.

I'm sorry....................................................for continuing this thread. :(
 
Sorry...
It's not been a good day so far!
Off on holiday tomorrow to the land where choc-block and leccy tape rules!
...and nobody dies!
Well, not many from electrocution anyway...
My parents used to have an apartment in Crete every summer we went their the additions to the wiring always made me laugh.
Choc blocks all over the floor spliced here there and everywhere with white flexes for outside lights , twisted tape joints for ceiling fans... all brand new work done over the winter
 
never had prob. with 3. 4 is tight and 5 is almost beyond it. once has to drill terminal oversize to get all in. allways remember, we are electricians, not wet-pants or wood butchers. there are no problems, only solutions.
 

Reply to 3 x 2.5mm T&Es into one 13A socket. How do you do it? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi Guys, I have quickly checked the forum and the net in general, I need a bit of advice regarding some solid core Aluminium twin and cpc. I am...
Replies
6
Views
1K
Hello. I am installing a CCTV system for my mum. It's a basic IP camera setup, with up to 4 cameras and a recorder. I plan to have the NVR in the...
Replies
4
Views
5K
I was going to call this thread spot the mistake but that would take up too much time, should be spot the correct bits This is a certificate from...
Replies
61
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock