Discuss 30 amp wylex rewireable fuse. in the Australia area at ElectriciansForums.net

E

entech

hi all, quick question ,... i have noticed that my ring circuits are wired in 2.5/1.5mm pvc/pvc and are protected by 30 amp re wireable fuses .. is this correct ???? as the max 2.5mm pvc/pvc can carry is 27 amps depending on install reference.

Cheers
 
The clue is in the word "ring". Circuit is fed from both ends hence the 30A rating of the device exceeding the cable if that makes sense?
 
thanks for the reply Ian. whats confusing me thou is that if you work out the design current and then decide on your fuse, then according to the osg you then select a cable which is equal to or exceeds the fuse selected. it doesnt differentiate for rings or radials does it??.

with your theory are you sort of saying that a ring wired in 2.5mm pvc/pvc could carry up to a max of 54 amps (2 x 27 amps)???
 
Hi mate because its a ring half of the current will flow down one leg and half down the other so the cable will not be overloaded so 2.5mm is ok with a ring circuit upto 32A
 
They say that we needed to reduce the apprenticeship to 3 / 4 yrs.
By the general questions I see posted on this site, we need to go back to the 6 yrs apprenticeships as the underpinning knowledge is sadly missing.
More time is need within the theory side of the qualification.
Anyone can run cable in and cut boxes into a wall. It ends there.
That when the knowledge comes into the great scheme of things
 
They say that we needed to reduce the apprenticeship to 3 / 4 yrs.
By the general questions I see posted on this site, we need to go back to the 6 yrs apprenticeships as the underpinning knowledge is sadly missing.
More time is need within the theory side of the qualification.
Anyone can run cable in and cut boxes into a wall. It ends there.
That when the knowledge comes into the great scheme of things

i was hoping that perhaps someone could point out exactly where in bs7671 it shows how to calculate cable sizes for ring final circuits.
 
i was hoping that perhaps someone could point out exactly where in bs7671 it shows how to calculate cable sizes for ring final circuits.

If you flip to the back of the big red book there are some useful diagrams that show both rings and radials, including radials and spurs off ring circuits. If you get on better with diagrams than descriptions these will be really useful. If you ran 2 lots of 2.5mm in parallel you would have 5mm total, giving you twice as much current carrying capacity. In basic form a ring is no more complicated than this. Your OSG also shows standard circuit layouts for domestic circuits. Don't know where exactly is mentions calculating rings specifically in the BRB but I was up at 5 this morning so going to bed - you'll have to trawl it yourself I'm afraid :)
 
If you flip to the back of the big red book there are some useful diagrams that show both rings and radials, including radials and spurs off ring circuits. If you get on better with diagrams than descriptions these will be really useful. If you ran 2 lots of 2.5mm in parallel you would have 5mm total, giving you twice as much current carrying capacity. In basic form a ring is no more complicated than this. Your OSG also shows standard circuit layouts for domestic circuits. Don't know where exactly is mentions calculating rings specifically in the BRB but I was up at 5 this morning so going to bed - you'll have to trawl it yourself I'm afraid :)

thanks cornburn. i had a look at the diagram in brb and it comes across well in diagram form.shows the spur fcu and non fused spur well also. will have a look for the ring calcs another day.

cheers again.
 

Reply to 30 amp wylex rewireable fuse. in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
304
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi, I have a product in which 5v 2.5 amp adapter (input 230vac 0.2 amp max) used. The adapter is burning out sometimes usually when I connect it...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock