Can any one tell me if i need to put rcd on 3036 cu if I am just changing socket faces cause i was told i did?
 
Last edited by a moderator:
Re: 1336 with rcd

I think you mean a CU with bs3036 fuses. In any case if you are only changing the faceplates that is considered a like for like replacement so no need to upgrade anything else on your installation
 
Re: 1336 with rcd

what if i have to replace socket boxes as well i was told by appoved nic guy that rcd was needed by law?
 
Re: 1336 with rcd

what if i have to replace socket boxes as well i was told by appoved nic guy that rcd was needed by law?


by law , oh my since when have the regs become law , the regulations are none statutory, all i would say is that its recomended that an RCD is in place . the ESC are trying to get every house hold protected by an RCD but as its existing then no , you need to provide a minor works cert as you may break the circuit and will need to be re tested once completed
 
One RCD covering the whole of the board as a main switch doesn't comply to 17th.. Does it?

And isn't the breaking capacity of 3036 1ka and my PFC is higher than this

replacement of face plates is not covered by 17th ed so rcd is irrelenant. suppliers fuse will back up breaking capacity so don't worry about it. don't forget to test circuit after changing plates and issue mwc.
 
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).

This was introduced to allow the UK continued use of BS3036 fuses which have breaking capacities of 1-4 kA.
 
im asking due to a PIR on this install.

cant identify the cut out rating and the tails look very small, from the cutout to the meter is 16mm, out the meter to CU looks smaller to me, poss 10mm..

also signs of overloading on lights, (cant see how though, only 5 pendants on the circuit)

and broken fuse carrier
and no cover on the front for the fuses
 

Attachments

  • IMG_1398.jpg
    144.5 KB · Views: 43
  • IMG_1397.jpg
    188.4 KB · Views: 47
I can't comment on the tails size from a photo.

The discolouring on the second white fuse carrier looks like 'flash' to me, from where a BS3036 has 'blown' on a fault.

They don't make 'em like that any more (thank god).
 
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).
not that its important for this post but i thought a 1361 was 33Ka

It is 33kA but the BS60439-3 UK annex only allows us to allow 16kA when used for this purpose.
 
The discolouring on the second white fuse carrier looks like 'flash' to me, from where a BS3036 has 'blown' on a fault.

That was my first thought but then noticed the customer had put 15a fuse wire in to replace the 5.

the tails had been doubled back in the terminals which is why i thought they were 10mm. could be one of the old dodgy size conductors.
 

Reply to 3036 with RCD in the Australia area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
380
Hi, I have a job for a customer, the consumer unit is an old 3036 board and there are several holes in it giving access to live parts, I can...
Replies
6
Views
711
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
759
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
452
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock