- Reaction score
- 9,025
I'm interested how you would all approach this one.
A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager have access.
One of the final circuits is protected by a 32A 3ph MCB and it supplies a 32 amp TPN socket adjacent to the board, the socket having it's own integrated RCD.
It took me a minute or two to realise it was failing RCD x1 tests because it was 0.3A not 0.03A.
Talking to the manager, it's used to supply an additional portable shower block using an armoured cable, for a couple of events a year.
The shower block has an all RCBO consumer unit , and the original installer (who I've spoken to) deliberately went with 300ma to provide selectivity.
When I put the front back on, there was a sticker saying "Requires 30ma downstream RCD protection" under the flap that I'd not noticed.
While I understand the rationale, as it stands it doesn't meet 411.3.3 ii) and I'd consider it a C2.
If there was a risk assessment in place stating who has control of the socket, and how it will be used, I might feel differently, but I only have the verbal assurance of the warden of what he will and won't do.
Am I being too harsh?
I'm still considering whether the best remedy is:
-change it for a time delayed 30ma device
-write a risk assessment putting the declared arrangements in writing.
-other?
Comments welcome.
A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager have access.
One of the final circuits is protected by a 32A 3ph MCB and it supplies a 32 amp TPN socket adjacent to the board, the socket having it's own integrated RCD.
It took me a minute or two to realise it was failing RCD x1 tests because it was 0.3A not 0.03A.
Talking to the manager, it's used to supply an additional portable shower block using an armoured cable, for a couple of events a year.
The shower block has an all RCBO consumer unit , and the original installer (who I've spoken to) deliberately went with 300ma to provide selectivity.
When I put the front back on, there was a sticker saying "Requires 30ma downstream RCD protection" under the flap that I'd not noticed.
While I understand the rationale, as it stands it doesn't meet 411.3.3 ii) and I'd consider it a C2.
If there was a risk assessment in place stating who has control of the socket, and how it will be used, I might feel differently, but I only have the verbal assurance of the warden of what he will and won't do.
Am I being too harsh?
I'm still considering whether the best remedy is:
-change it for a time delayed 30ma device
-write a risk assessment putting the declared arrangements in writing.
-other?
Comments welcome.