Discuss 32a three phase isolator neutral bar? in the UK Electrical Forum area at ElectriciansForums.net

As it's for a trainee I'll just add that if it's a Neutral contact will be early make / late break compared to the L1, L2, L3 contacts.
But I'll leave them to find out the importance of that.
 
Last edited:
Even magnified it doesn't appear to have a marking on the 4th contact, jut the arrow in the plastic case.
From the style (plastic screws) it looks to be a Europa, which also appears very similar to older Klockner style disconnectors.
There's space on the left side for another contact so it may be that the 4th contact is auxiliary and could have a 5th.
The 4th contact will have details on the side.
 
Last edited:
Even magnified it doesn't appear to have a marking on the 4th contact, jut the arrow in the plastic case.
From the style (plastic screws) it looks to be a Europa, which also appears very similar to older Klockner style disconnectors.
There's space on the left side for another contact so it may be that the 4th contact is auxiliary and could have a 5th.The 4th contact will have details on the side.
32A 4 Pole Surface Mount Isolator IP65 - https://www.yesss.co.uk/32a-4pole-surface-mount-isolator-ip65 It's one of those. We're basically using them as an emergency stop.
 
No it's just bare. The guys i am working with said it was the N though. Incidentally we were hooking up machines with no neutral anyway.

It's an 'Eris Industrial' 32a/20a from Yesss.
Strictly speaking the neutral is the separate terminal on the enclosure. The fourth switch terminal I would consider an auxiliary as it is not marked for a specific purpose and can be used for several things.
 
Strictly speaking the neutral is the separate terminal on the enclosure. The fourth switch terminal I would consider an auxiliary as it is not marked for a specific purpose and can be used for several things.
Is there any advantage/disadvantage to the way we've done it? The machinery we're hooking up doesn't use neutral so it's not used anyway.
 
From the link above it's shows switched neutral

32a isolator.PNG
 

Reply to 32a three phase isolator neutral bar? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
459
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
859
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
374
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
859
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock