Discuss 350 ohms on sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

boycie

probably another school boy error from a Electrical Trainee but i was testing a ring and 2 sockets were throwing out a reading of 350 ohms. zs was ok though. any ideas regarding this would be niceeeeeeee !!!
 
Just because it has a good Zs doesn't mean it's a ring! Check the end to end of L N and Cpc, whichever one is the high reading, could be both, check terminations at each socket. Could be screwed down on Insulation
 
why would you power up to read Zs with such a crappy continuity reading?
 
OK. if it's just at 1 socket, pull the socket off and measure on the cables. that will prove a bad connection or a dodgy socket.
 

Reply to 350 ohms on sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
525
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
799
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock