Discuss 3p breaker feeding 3 x 1p circuits in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
10
Hi everyone.

I may be blind but I can't find a definitive answer.

Can I use a 3 pole breaker (originally feeding a massive 3 phase heater) to feed 3 single phase circuits?

I've run seperate neutrals for the 3 new circuits and the breaker is rated for the load required - 30a per phase (I'd be installing 3 x 32a breakers if I could, but the age of the board makes this a pain).

Killing all the circuits in the event of a problem won't be an issue - they're all in my workshop.

So - is it permitted?

There are no socket outlets involved
 
It will still function as would a single-pole device but you will lose three circuits if a fault occurs on one. Not the end of the world but probably falls foul of Reg 314.2, what make is the board.
 
Not worried about losing 3 circuits in the event of a fault. Board is a square D circa 1990 full of old black QO breakers.

The whole installation is going to be inspected so it needs to be right - or at least acceptable.
 
Problem with the device you have reused is that it is a Type 4. How have you proved disconnection times will be met.
 
A fault on one circuit shouldn’t effect another circuit?
Also because they are all on the same ocpd would it be classed as one circuit not 3?
 
Oh cool - saw those they're not exactly the same but the look like they'd fit.

I've attached an image - I'm replacing the top 3p breaker.
IMG_20190706_182822.jpg
 
ÂŁ14. that's cheap.had to get a 32A 3p QO MCB for a garage rolling road. ÂŁ116 + VAT.
 
ÂŁ14. that's cheap.had to get a 32A 3p QO MCB for a garage rolling road. ÂŁ116 + VAT.
I don't think Schneider continued the production of the triple-pole devices for very long.
 
if i remember, the rolling road was fed from a 20A 3 phase MCB with a 6.0mm SWA. clowns came and installed a new machine 27A/phase and wondered why it was tripping out on load.
 
if i remember, the rolling road was fed from a 20A 3 phase MCB with a 6.0mm SWA. clowns came and installed a new machine 27A/phase and wondered why it was tripping out on load.

And the same clowns were still sat there in the van trying to drive home
 
"Quick! Put your foot down, tel is coming and he's wrapped in a floral blanket"
 
He turned his back on them
 

Attachments

  • 8B85F19C-92AA-409A-8E7E-103778760D2A.jpeg
    199.9 KB · Views: 4

Reply to 3p breaker feeding 3 x 1p circuits in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
426
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello. So, I would like to know how I can choose the correct circuit breaker value when doing a new installation. My example is: I have 16...
Replies
2
Views
873
Hello, I have an old 16A Wylex SK type B plug-in breaker in the fuse box in my garage which keeps tripping, and every time (and only at that time)...
Replies
5
Views
2K
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock