Hi everyone.
I may be blind but I can't find a definitive answer.
Can I use a 3 pole breaker (originally feeding a massive 3 phase heater) to feed 3 single phase circuits?
I've run seperate neutrals for the 3 new circuits and the breaker is rated for the load required - 30a per phase (I'd be installing 3 x 32a breakers if I could, but the age of the board makes this a pain).
Killing all the circuits in the event of a problem won't be an issue - they're all in my workshop.
So - is it permitted?