Hi there...

Bit out of practice with 3phase design, and want to learn more.

Just want to check if this would be correct:

Ib = KW/V*1.732

Many thanks,

Sy
 
Hi there...

Bit out of practice with 3phase design, and want to learn more.

Just want to check if this would be correct:

Ib = KW/V*1.732

Many thanks,

Sy

Yes, as long as there is no power factor :)
and watts not kW

The equation you are rearranging is actually
total power(W) = √3*Vl*Il*PF

you are using Il to be your Ib value and Vl = 400
 
Last edited by a moderator:
Thank you for your help there,

Power factor will definately be invloved in the example I'm looking at.... as it has a motor.

Time for a bit more investigation, I will probably be back:)

Cheers Sy....
 

Reply to 3phase help please.... in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi I have a 3phase shop in a high humidity area in (Hawaii) and I'm having some issues with low voltage on the single phase outlets on the 120v...
Replies
6
Views
924
Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
1
Views
405
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
872
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
813
Hello respected members, Looking to gain practical electrical experience in the London area preferably commercial but will consider domestic as...
Replies
1
Views
745

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock