schoe

Does anyone no where I can get one from or if they exist. can you get them in a grid system which will fit in a 2 gang back box?

Thanks chris
 
I'm not sure of the terminology, are you trying to find a switch assy with 4 dimmers on the same gridplate?
 
Yeah sorry. I need either 4 dimmers on one switch capable of Switching 600 watts per dimmer.

Or a grid plate which will do the same, but will fit in a 2 gang back box. Hopefully that's a bit clearer.
 
Thanks for patiently clarifying. I don't know if the hardware exists but the heat load from four dimmers equalling 2.4kW in the same 2-gang back box will cause premature failure if it's not very well ventilated. Is there no way you can use tactile dimmers (4 wire modules) and mount them remote somewhere where there's more air movement?
 
The wires have already been run and tested. I have four circuits of spots in a kitchen. 2 circuits carry 450 watts one carries 600 watts and the fourth carries 250 watts. The customer ideally wants them all on one switch or on a grid plate. I've chopped a 2 gang box into the wall thinking I could fit all the dimmers in that using the grip plate. But from what your saying it doesn't seem possible so I'll just have to chop another back box in and have two 2 gang switches.

Thanks anyway

Chris

From what your saying this prob isn't
 
i ve seen the 4 wire onees,as somone said above, i have the same issue no doubt will be next week he be asking me again, i have 12 spots on one of my switches= 600 watts do these need to be rated at 1000W
 
The wires have already been run and tested. I have four circuits of spots in a kitchen. 2 circuits carry 450 watts one carries 600 watts and the fourth carries 250 watts. The customer ideally wants them all on one switch or on a grid plate. I've chopped a 2 gang box into the wall thinking I could fit all the dimmers in that using the grip plate. But from what your saying it doesn't seem possible so I'll just have to chop another back box in and have two 2 gang switches.

Thanks anyway

Chris

From what your saying this prob isn't

A 600w dimmer for 600w of downlights wont last long.You need to up the size for downloights
 

Reply to 4 gang 2 way 600 watt dimmer in the Australia area at ElectriciansForums.net

Similar Threads

Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...
Replies
2
Views
238
This is confusing, I've ordered a few bits of this stuff, some switch modules and front plates and in the bumf on the website it says:- Click...
Replies
5
Views
344
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
629
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
Hi all, I am upgrading my traditional 2 gang light switch in the kitchen to a smart 2 gang dimmer switch. When I wired up the switch the switch...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock