Hi all

From the outset I'm not in an electrician. I am posting here because I'm thinking the subject matter is quite specific and will prob require some historic knowledge/ experience - I'm hoping someone will allow me to benefit from their knowledge.

I am converting a Bradbury 4 post lift (a variation of a liftmaster 735, which I think is a mk1/2) from 3 to single phase - single direction motor.

The issue I have is with the Dol starter. I want to replace the 415v original with a 230v dol starter with overload. The original dols is housed within the oil reservoir and the (dols') on/off buttons are 'pushed' via a mechanical rod & linkage setup connected to the up/down lever on the main post.

I'm thinking I need to either retain the original dol metal enclosure, replacing it's innards OR replace the entire box.

Simplest would appear to be to retain the original enclosure - thus retaining the mechanical on/off linkage - problem would be the successful marriage of the enclosure on/off buttons with the new internals.

Anyone thoughts/ experience/ solutions of/ for this scenario more than gratefully received.

photos attached (hopefully)-
 

Attachments

  • Screenshot_20220212-101242.png
    2.1 MB · Views: 52
  • Screenshot_20220212-131604.png
    1.7 MB · Views: 43
  • Screenshot_20220212-131619.png
    1.5 MB · Views: 44
I have a few thoughts, based on a series of assumptions that might quickly collapse like a house of cards! But to get the ball rolling....

I'm first assuming that in original 3 phase mode the Down operation basically opens the hold-on contact to ensure the motor is stopped, and also simultaneously operates the hydraulic recirculation valve mechanically.
So first principles are that you trying to energise the pump for UP, and for DOWN you are trying to mechanically recirculate the hydraulics while ensuring the pump isn't running.

I can't really see from the photo's exactly how it works, but my further assumption is that the UP operation originally manually closed the contactor while energising the coil to hold the contactor there?

If so my thinking would be to leave the original starter in place, using it as a simple two wire "make" switch that closes contacts when the control handle is moved to "UP" and in all other states the contacts would be open.
These could be used to energise a new contactor for the new 230v pump.
You would then be holding the lever in the UP position to ascend, let go and the pump would stop.
Down would be purely mechanical using the existing setup.

Apologies if I've misunderstood how it works. There are finer minds than mine on this forum that in due course I'm sure will have more ideas. ( @pc1966 @Lucien Nunes ).
 
I have a few thoughts, based on a series of assumptions that might quickly collapse like a house of cards! But to get the ball rolling....

I'm first assuming that in original 3 phase mode the Down operation basically opens the hold-on contact to ensure the motor is stopped, and also simultaneously operates the hydraulic recirculation valve mechanically.
So first principles are that you trying to energise the pump for UP, and for DOWN you are trying to mechanically recirculate the hydraulics while ensuring the pump isn't running.

I can't really see from the photo's exactly how it works, but my further assumption is that the UP operation originally manually closed the contactor while energising the coil to hold the contactor there?

If so my thinking would be to leave the original starter in place, using it as a simple two wire "make" switch that closes contacts when the control handle is moved to "UP" and in all other states the contacts would be open.
These could be used to energise a new contactor for the new 230v pump.
You would then be holding the lever in the UP position to ascend, let go and the pump would stop.
Down would be purely mechanical using the existing setup.

Apologies if I've misunderstood how it works. There are finer minds than mine on this forum that in due course I'm sure will have more ideas. ( @pc1966 @Lucien Nunes ).
Thanks Tim

You are way ahead of my basic understanding of the existing set up. I think your assumptions are correct. However the existing circuitry is not working.

I purchased the lift 10 years ago - erected it, parked a car on it and then life got in the way. A few weeks ago I cleared the debris, bought a single phase motor & wired it up using existing dols and fused rotary isolation switch (mounted externally to the oil reservoir)

On investigation I found the internals of the rotary isolator to be stripped - it could not have functioned - so replaced.

I have wired the now working isolator to the single phase motor via the existing dols. I have no output (from the dols') to the motor so assumed either fried (like the isolator) or not working due to lack of 230v coil.

I appreciate your time and certainly do not wish to waste it - would any additional photos be of help to you?

Si
 
The starter coil appears to have four leads, which suggests it might be dual voltage. Check any attached labels e.g. inside lid for evidence to that effect. Also check whether the overload relay will adjust to the FLC of the single-phase motor. It probably won't but worth ruling that out before you start modding.

Failing that you can probably use the start and stop contacts in the original starter to control the new one. This will require testing the internal configuration to identify the correct terminals. Are you armed with a multimeter?
 
I have wired the now working isolator to the single phase motor via the existing dols. I have no output (from the dols') to the motor so assumed either fried (like the isolator) or not working due to lack of 230v coil.
I'd split this into stages, first check the UP lever manually closes the contactor.
More assumptions.....
You should find that the top row of 3, A B and C are respectively joined to the bottom row of 3 when UP is activated. Check with a multimeter on the continuity setting. So A should show continuity to the one under it, B should show continuity to the one under it etc. You might need to extend wires out of it to test this. (Obviously this is all with power off!)

I suspect the top right hold-on terminal is permanently joined to one of the top 3 internally, most likely the terminal marked C.
Again, check this with a multimeter. As originally configured this would send 400v to the coil once the contactor closed.

Once these principles are confirmed it is possible to wire it for 230v, subject to the coil being dual voltage as Lucien suggested.
 
I'd split this into stages, first check the UP lever manually closes the contactor.
More assumptions.....
You should find that the top row of 3, A B and C are respectively joined to the bottom row of 3 when UP is activated. Check with a multimeter on the continuity setting. So A should show continuity to the one under it, B should show continuity to the one under it etc. You might need to extend wires out of it to test this. (Obviously this is all with power off!)

I suspect the top right hold-on terminal is permanently joined to one of the top 3 internally, most likely the terminal marked C.
Again, check this with a multimeter. As originally configured this would send 400v to the coil once the contactor closed.

Once these principles are confirmed it is possible to wire it for 230v, subject to the coil being dual voltage as Lucien suggested.
Tim, Lucien, thank you - I will do as suggested tomorrow & revert.
Si
 
I'd split this into stages, first check the UP lever manually closes the contactor.
More assumptions.....
You should find that the top row of 3, A B and C are respectively joined to the bottom row of 3 when UP is activated. Check with a multimeter on the continuity setting. So A should show continuity to the one under it, B should show continuity to the one under it etc. You might need to extend wires out of it to test this. (Obviously this is all with power off!)

I suspect the top right hold-on terminal is permanently joined to one of the top 3 internally, most likely the terminal marked C.
Again, check this with a multimeter. As originally configured this would send 400v to the coil once the contactor closed.

Once these principles are confirmed it is possible to wire it for 230v, subject to the coil being dual voltage as Lucien suggested.

Tim, Lucien, thank you - I will do as suggested tomorrow & revert.
Si
Tim, Lucien
Tim, Lucien, thank you - I will do as suggested tomorrow & revert.
Si
Tim, Lucien

I'm attaching numerous photos which may/ may not prove useful.

Mechanical external 'up' mechanism appears to close contact (top right, beneath wheel) - but no continuity across A-L1, B-L2, C-L3 when closed

I have manually closed the coil contact and have continuity across A-L1, B-L2,C-L3.

No continuity between top right terminal (1) and any of A,B or C.

Does this help?
 

Attachments

  • IMG_20220213_174312832.jpg
    299.7 KB · Views: 24
  • IMG_20220213_174301619.jpg
    342.9 KB · Views: 22
  • Screenshot_20220213-171426.png
    1.6 MB · Views: 26
  • Screenshot_20220213-171420.png
    1.6 MB · Views: 26
  • Screenshot_20220213-171408.png
    1.8 MB · Views: 25
  • Screenshot_20220213-171403.png
    1.7 MB · Views: 26
Another 4 post Bradbury ramp owner here!
Mine was also 3 phase, now converted to single phase, but I didn't change the motor. It was dual voltage, so reconfigured to the lower voltage, with a capacitor to simulate the missing phases, plus another capacitor and current operated switch to provide starting torque. Mine appears to be a newer model than yours, because the original contactor was a more modern type, which I merely changed for a similar one with a 240 volt coil. Been in use and running fine now for about fourteen years.
Regarding your pics in your last post, if the last pic is the single phase converted final version, the incoming neutral should be connected directly to the isolator, bypassing the fuse. The fuse in the live wire should be retained.
 
Another 4 post Bradbury ramp owner here!
Mine was also 3 phase, now converted to single phase, but I didn't change the motor. It was dual voltage, so reconfigured to the lower voltage, with a capacitor to simulate the missing phases, plus another capacitor and current operated switch to provide starting torque. Mine appears to be a newer model than yours, because the original contactor was a more modern type, which I merely changed for a similar one with a 240 volt coil. Been in use and running fine now for about fourteen years.
Regarding your pics in your last post, if the last pic is the single phase converted final version, the incoming neutral should be connected directly to the isolator, bypassing the fuse. The fuse in the live wire should be retained.
Cheers Bri, thanks - I've been in and out of this for months, sometimes minutes at a time, I can't even explain why I did that when I did it and even more confusing, when I took the photo why I didn't see it.
Si
 
The operating controls on mine are two push buttons and a lever. The ramp, when in use doesn't rely on the hydraulic ram to keep it in position - there is a metal bar alongside the ram housing which has rectangular holes in it about every two inches, you raise the ramp slightly higher than you need, then lower it slightly, and a solenoid operated peg pushes into the hole in the bar that is along side it, taking the entire weight of the ramp bed and whatever is on it.
The LH push button on the control panel starts the motor/pump, retracts the peg, and raises the ramp. You then release the button, pull the lever downwards, and the ramp lowers slightly onto the peg.
To lower the ramp, you push the fist button momentarily to raise the ramp slightly and take the load off of the peg. Next, you push the RH button, which powers the solenoid that retracts the peg. This button is held in, and the lever pulled down, which opens the oil return valve, allowing the ramp to descend. To stop the ramp part way down, you release the RH button, peg goes in, then you release the lever, when the peg reaches the bottom of its 2" hole.
Does yours work the same way?
 
The operating controls on mine are two push buttons and a lever. The ramp, when in use doesn't rely on the hydraulic ram to keep it in position - there is a metal bar alongside the ram housing which has rectangular holes in it about every two inches, you raise the ramp slightly higher than you need, then lower it slightly, and a solenoid operated peg pushes into the hole in the bar that is along side it, taking the entire weight of the ramp bed and whatever is on it.
The LH push button on the control panel starts the motor/pump, retracts the peg, and raises the ramp. You then release the button, pull the lever downwards, and the ramp lowers slightly onto the peg.
To lower the ramp, you push the fist button momentarily to raise the ramp slightly and take the load off of the peg. Next, you push the RH button, which powers the solenoid that retracts the peg. This button is held in, and the lever pulled down, which opens the oil return valve, allowing the ramp to descend. To stop the ramp part way down, you release the RH button, peg goes in, then you release the lever, when the peg reaches the bottom of its 2" hole.
Does yours work the same way?
Bri

I remember reading how it works (year, maybe years ago) and will have notes somewhere - from memory, simpler than yours - lever up for up, mechanical lock to hold, lever down returns fluid to tank, lowering lift.
Trying to take it one step at a time - getting it to move 1st.
It came in parts - trying not to be too optimistic seeing as the rotary switch internals were literally in bits.
 
Mechanical external 'up' mechanism appears to close contact (top right, beneath wheel) - but no continuity across A-L1, B-L2, C-L3 when closed

I have manually closed the coil contact and have continuity across A-L1, B-L2,C-L3.
I haven't been able to understand from photos how the lever moves the contact, but is there any adjustment facility? It sounds as though it is supposed to fully close the contact.
 
I haven't been able to understand from photos how the lever moves the contact, but is there any adjustment facility? It sounds as though it is supposed to fully close the contact.
Sorry Tim, I should have provided an explanation to accompany photos. Moving the [post mounted] lever operates (through mechanical linkage) a mechanical spring loaded 'pivot' attached to the Dol starter front cover - which depresses the button (eg green - if lever up) on the Dol starter enclosure. Both buttons have rods attached to their rear - green is the shorter. The green button rod depresses the spring loaded contact plate below the adjustment wheel and completes circuit. I will take a close look to see if I can adjust rod length - if that's what you mean. - I could also wire it up and carefully depress contact manually with cover off - make sense if knew wiring ok first?
 

Attachments

  • Screenshot_20220213-220207.png
    1.3 MB · Views: 20
  • Screenshot_20220213-220143.png
    1.3 MB · Views: 19
Looks like you're going to have the problem of either finding a 230V coil for that contactor, or arranging a modern contactor so that it can be operate by the existing mechanical linkage.
Could possibly be solved by a panel mounted pushbutton, as on mine, and two handed operation.
 
It would be a doddle to start again with a new 230v starter and an auxiliary safety button for the UP operation as Brian said.
The main question in my mind now is how "Down" works....I had imagined the DOWN lever was also operating a mechanical oil return, but now the principle of the lever and the rods has been explained I'm shifting to believing it's an electrically operated return valve?
Maybe annotating the photo of the inside of the DOL would help, showing exactly what UP and DOWN are pressing inside.
I'm thinking that as well as interrupting the coil, DOWN must close two contacts somewhere too.
 
If the OP's ramp uses a solenoid operated latch to lock the ramp in position, like mine, and is single lever operated, then there must be contacts to power that solenoid when the lever is pushed down.
It's unlikely that the oil release valve is electrically operated, because that would make it either fully closed or fully open, and wouldn't allow the descent speed of the ramp to be controlled.
 
When I bought mine, it had been under three feet of floodwater a couple of weeks earlier!
Brian, Lucien, Tim

I'm not very good at leaving things I don't completely understand so before I move on to resolve the practical issue of incorporating a 230v dols would someone please confirm the correctness of my wiring diagram.

I am attaching an image of the Dols and my basic wiring diagram interpretation of it. I have coloured in live & neutral to distinguish them from hardwiring.

2 things (I am aware of) I don't understand:
1, why 2 of the wires exiting the coil join at a terminal?; and
2, assuming I can use 'L3-C as I have to provide current to the off switch (NC) when on switch (no) released, any idea how I would facilitate the 'orangey '(on diagram) connection to C?

Ps. The purple highlighted circle on the wiring diagram indicates the rocker that opens the off switch (NC) operated by the red button.

Of course I could have it all wrong!

Won't let me add images- to follow hopefully

Thanks again.

Si
 
Brian, Lucien, Tim

I'm not very good at leaving things I don't completely understand so before I move on to resolve the practical issue of incorporating a 230v dols would someone please confirm the correctness of my wiring diagram.

I am attaching an image of the Dols and my basic wiring diagram interpretation of it. I have coloured in live & neutral to distinguish them from hardwiring.

2 things (I am aware of) I don't understand:
1, why 2 of the wires exiting the coil join at a terminal?; and
2, assuming I can use 'L3-C as I have to provide current to the off switch (NC) when on switch (no) released, any idea how I would facilitate the 'orangey '(on diagram) connection to C?

Ps. The purple highlighted circle on the wiring diagram indicates the rocker that opens the off switch (NC) operated by the red button.

Of course I could have it all wrong!

Won't let me add images- to follow hopefully

Thanks again.

Si
 

Attachments

  • Screenshot_20220214-221003.png
    1.4 MB · Views: 17
  • Screenshot_20220214-220520.png
    1.3 MB · Views: 19

Reply to 4 post Bradbury liftmaster dol starter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all I would like a bit of advice to do with a DOL starter ill be fitting. Basically I'm replacing an old water damaged crabtree DOL starter...
Replies
8
Views
2K
Hi all. I'm looking to build myself a rig with a small single phase motor and learn a bit more about motor controls etc. I mostly do domestic and...
Replies
34
Views
3K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
It's not that often I stare stupidly at something for 5 minutes and can't work out where to start, but.... The horizontal and lower vertical...
Replies
9
Views
2K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock