- Reaction score
- 8,885
First of all welcome! I hope the above doesn't make too painful reading - there are certainly gentler ways to join a forum!Hello all.
I'm the first guy.
I couldn't fit the oven not because I refused to but because I was on holiday.
Are those saying you need 6mm on a clipped direct no derating factor 32a circuit saying they disagree with the iet table? I'm not trying to be argumentative, I'm just following the book. Surely the iet have checked these as a long term load.
Cheers
Gc
There were some early responses before the fact it was clipped direct came to light. After that I think there was a consensus that it was compliant and you'd done nothing wrong(!).
It's true that a few of us (myself included) did express some surprise mainly because it's not something we encounter too often.