Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen.

Cables will run through a combination of uninsulated platerboard ceiling, down the wall behind dot n dab plasterboard and in enclosed plaster where channels are repaired.

The online cable size calculators I've found don't show 'buried in plaster' as a criteria so is that considered more thermally insulated than say a stud wall or in an insulated cavity?

The oven is rated at 3.4kW - the MCB in the CU feeding the existing (same rating) is 32A and it looks like it's connected using 4mm cable (distance is about 6 metres. I'm assuming, as the original set up has been OK for years, the MCB and cable size are OK.

The new induction hob spec sheet says 'power load' 7.35kW and 'minimum power or fuse size = 32A'. It's been suggested it needs it's own supply and has to be 'hard wired'. So my questions are:

1) I've read somewhere that a diversity factor for the induction hob shouldn't be applied where the manufacturer states a specific load (i.e. 7.35kW and the minimum protection @ 32A), is that correct?

2) If 1) above isn't true, does the induction hob actually need to be on a separate supply from the CU or would an applied diversity factor mean the 32A existing supply and 4mm cable would be adequate for both oven and hob?

3) It's no hassle to run a dedicated supply for the hob so if I did so, given the cable routings I've listed above (distance also around 6m), will a 32A MCB in the CU and 6mm cable be OK (seems to be the size recommended in the online calculators unless in a heavily insulated environment) .

Really appreciate your anticipated feedback.
 

Reply to Cable sizes for fan oven and induction hob in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
Replies
1
Views
628
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
Replies
2
Views
2K
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
947
Hello, Looking at changing out my gas hob for the PIV851FB1E Bosch Induction Hob. The Induction hob is 7400W and by my calculations this would...
Replies
3
Views
2K
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock