Discuss MCB size and wire size for an electric oven and induction hob in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hello

I have two new appliances
Electric oven rated at 3.95 KW
Induction hob rated at 7.2 KW

total of 11.15 KW

Currently it is on its own supply with a 10mm Twin and Earth and the MBC is 32amps

Can you please advise if the following

Cable size is sufficient ( behind plaster )

MCB Amp needed and can I use the new ones now as my cu is old

Thanks in advance
 
Diversity for a domestic oven/hob is usually taken as 10A + 30% of the remainder.
11150W = 48.5A, so 10A + 30% of 38.5A = 21.5A.
Thank you for your reply, so I don't really want to run a separate circuit to split the oven and hob up.

so with this calculation do you think I am ok ?

Would you upgrade the MCB to 40Amp or 50Amp

I have and older contactum

thanks
 
Thank you for your reply, so I don't really want to run a separate circuit to split the oven and hob up.

so with this calculation do you think I am ok ?

Would you upgrade the MCB to 40Amp or 50Amp

I have and older contactum

thanks

The calculation that Brian did for you took into account both appliances.
 
I tended to treat a job and oven as two separate appliances, when applying diversity’s, but with only my thumbs to count on, still think that’s ok?
 

Reply to MCB size and wire size for an electric oven and induction hob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
651
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Replies
0
Views
879
Hello, Looking at changing out my gas hob for the PIV851FB1E Bosch Induction Hob. The Induction hob is 7400W and by my calculations this would...
Replies
3
Views
2K
Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
Replies
1
Views
628

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock