Discuss PIV851FB1E Bosch Induction Hob Install in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello,

Looking at changing out my gas hob for the PIV851FB1E Bosch Induction Hob.

The Induction hob is 7400W and by my calculations this would be 7400/230=32.2A

Was after advice on the best method for install.

Can this be powered direct from the CU with appropriate MCB or is it necessary to have a cooker switch adjacent to the induction hob. Either at worktop level or in a cupboard underneath.

The distance from the CU is around 15m and the cable would be clipped to the joists under the flooring. At the wall it would be behind the plaster board.

Would appreciate advice on appropriate MCB size and cable diameter etc.

Thanks in advance for any advice given.
 
6mm and a 32A MCB should be fine for that hob, even 4mm maybe, it wont ever draw its maximum current all at once and the 7.4kW is probably measured at 240V not 230. Needs RCD protection at consumer unit, RCD or RCBO. I don't actually think there is a reg saying you need a local isolator but we always put one in, usually inside a nearby cupboard, 45A switch, use a double size switch though, they are so much easier to fit.
 
6mm and a 32A MCB should be fine for that hob, even 4mm maybe, it wont ever draw its maximum current all at once and the 7.4kW is probably measured at 240V not 230. Needs RCD protection at consumer unit, RCD or RCBO. I don't actually think there is a reg saying you need a local isolator but we always put one in, usually inside a nearby cupboard, 45A switch, use a double size switch though, they are so much easier to fit.
@oscar21
Apologies for late reply and thanks. Been travelling a bit. Another question though. With this being an Induction Hob what would the curve type be for the RCBO.
 

Reply to PIV851FB1E Bosch Induction Hob Install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
948
Hi all I'm in the process of swapping out my 4 zone CDA induction hob for a 5 zone Bosch. Currently the existing wire starts as a 5 core cable...
Replies
10
Views
2K
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
4K
Hi, Just looking for a bit of advice here. I am considering swapping my existing 4 burner gas hob for a Bosch induction one. I am not proposing...
Replies
10
Views
5K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock