Discuss Zanussi 7.35kW induction hob power cable in the DIY Electrical Advice area at ElectriciansForums.net

Dickiem

DIY
Reaction score
1
Hi all,

I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied with a power cable and the manual says it needs connected using a H03V2V2-F or H05BB-F cable with a temperature withstand of 90 deg C minimum. I’ve had a look on t’internet and am struggling to find anything above 2.5mm cable at that spec. The terminations in the hob look like they’ll struggle to accept much above that but with diversity, any thoughts on whether 2.5mm would cope?
 
Last edited:
2.5 is adequate. even without diversity applied, 7.5 kW = 31A.
 

Reply to Zanussi 7.35kW induction hob power cable in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
807
The manufacturers instructions for an induction hob I will be fitting in the new year are telling me to use either H03V2V2-F or H05BB-F (basically...
Replies
17
Views
11K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K
At the moment I have a stand alone cooker – it is an electric oven with gas hobs. I want to get rid of this and extend my kitchen worktop to put...
Replies
29
Views
59K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock