Discuss 4mm half of circuit on 32a mcb in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
29
Hi all,
I did some work on a house the other day that had a circuit for sockets which was cabled in 4mm to half way in the house the split of it to 2.5 up to the sockets. It had a 32a breaker. I'm aware that you can have a 32a 4mm radial but that the whole circuit must be in 4mm. Using 2.5 on any part of the radial is not really acceptable am I right?
 
You can only have one double socket on a 2.5mm cable @32A it's no different to a spur, change the breaker to 20A if any more than one on 2.5mm radial
 
As far as I know you can't buy a bigger fuse than 13a for a plug top x 2 = 26A perfectly controlled cable rating, so many sparks afraid of the limits, if you're under you're under

Never liked the idea of relying on forward fusing, like to design a circuit fit for purpose, with your principle you might as well back it with a 45amp breaker.!!
 
are you sure this wasn`t a hybrid circuit here...?

I suppose it was kind of hybrid. It was a bungalow with one socket circuit which included all sockets and the kitchen... So the circuit does have a fair amount of 2.5 in it but also has quite a lot of 4mm as well. It's not burnt down so far, I told the customer they didn't seem that bothered.
 
You sure the 2.5’s are spurs? Sounds like a lollipop to me.

It might have been. I only had to work on one socket which had only one piece of 2.5 going to it from the piece of 4mm from the board. I since changed that one to 4mm I could see under the floor another junction box with another spur in 2.5 going up. Just never seen this before. Wasn't able to check any of the other sockets.
 
Lollipop_zps118a7755.jpg

Quite handy for largish buildings. Run a 4/6mm from the CU to where the ring is needed. Great for confusing the youngsters.

I think we used 6mm when we got around to rewiring the brothers 4 floor + basement house. Both of us electricians, it only took three years to finish.
 

Reply to 4mm half of circuit on 32a mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
230
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
695
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
819
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock