Search the forum,

Discuss 4mm radial from ring feeding CUs in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Afternoon all,

my boss is trying to have me sign off a job someone has done.
4mm radial off a ring main feeding 2 CUs in shed all MCBd correctly. RCD protected. NOT FED OFF FUSE SPUR

Is there any reg this may no satisfy. It all seems okay due to ratings of cable etc but I’m not confident

thanks
 
It does not comply, and is pretty terrible installation design to boot.

You cannot feed more than one point from an unfused spur, being 4mm doesn't change this. The setup you have will concentrate a heavy load on one point of the ring which is non compliant and can cause excess current to flow in one side of the ring.
 
Afternoon all,

my boss is trying to have me sign off a job someone has done.
4mm radial off a ring main feeding 2 CUs in shed all MCBd correctly. RCD protected. NOT FED OFF FUSE SPUR

Is there any reg this may no satisfy. It all seems okay due to ratings of cable etc but I’m not confident

thanks
I you are unsure don't sign from what I can see from your post, your boss is asking you to commit professional suicide mate. Walk away, stick to your guns wrongful dismissal will be you're defence, should he try to sack you. Why would any sane Electrician agree to agree to a 4mm2 cable from a RFC IN 2.5mm cable ludicrous suggestion.
 
I totally agree is awful design and my boss being qualified up to the 14th edition at most.

thanks for your inputs I’ll pass the message on ?
Does your Boss belong to a CPS Provider? If yes he should know better.
 
Last edited:
When you say sign off for someone else is it a job by a third party and not the company that employs you.
 
Only way of this install being complied is a spur supplying the 4mm which is what I can only recommend before touching it
Why would you spur a spur with 4mm from an RFC of 2.5MM don't make any sense whatsoever.
 
Sorry got my termination wrong. Supply the 4mm from a fused spur off the RF
[automerge]1597157581[/automerge]
When you say sign off for someone else is it a job by a third party and not the company that employs you.
My boss has basically sold this person all the gear to install himself and told him our company would sign off which I’m not happy about whatsoever
 
Sign it off as “M. Mouse” or “ D. Duck”

I’ve heard companies having one trained guy go around signing off everyone’s jobs.... but that’s other electricians (still shouldn’t be done)
What your boss is asking you to do is sign off a DIYer.

Sign your boss’s name.
 
If you are the third party ready to do the sign off, I would be walking away in any condition of the work.Why did your boss not get you the job.? Does the person who did the job work for him too.?
 
Sorry got my termination wrong. Supply the 4mm from a fused spur off the RF
[automerge]1597157581[/automerge]

My boss has basically sold this person all the gear to install himself and told him our company would sign off which I’m not happy about whatsoever
Niether would I mate the Boss is a chancer, more interested in a fast buck, than doing the right thing, get another job, or go self employed better than working for a Muppet that would be willing to use you as a scapegoat for his incompetence, contact the CPS Provider if he belongs to one.
[automerge]1597158995[/automerge]
I wish I knew the answer to that ?? tbh I’m miffed off at being put into Thai situation
Maybe a daft question, but do you belong to a trade association TU or any such organisation
'
[automerge]1597159114[/automerge]
I wish I knew the answer to that ?? tbh I’m miffed off at being put into Thai situation
Matey, your Boss wants outing as a Cowboy, the sooner the better.
 
Last edited:
IMO you have 3 solutions.
1 walk away and refuse to put your name to it.
2 fit a 13amp sfu adjacent the socket off the ring. (not a great design with all the accessories installed in the shed a waste)
3 Run a suitably sized cable back to the origin of the supply. (sub main)
 
You shouldn’t have to alter or install anything as you have not installed it , only signing it off as compliant with bs7671, so to me you have only one option, refuse to certify it.
Tell your boss to do it, as he’s the one who said his company will certify it.
 
IMO you have 3 solutions.
1 walk away and refuse to put your name to it.
2 fit a 13amp sfu adjacent the socket off the ring. (not a great design with all the accessories installed in the shed a waste)
3 Run a suitably sized cable back to the origin of the supply. (sub main)
Option 2 is the only option to keep everyone happy but me ???
 
Tell your boss to sign it off.
Why do we get "we ran into some problems", when we try r/to access the responders reply, makes a nonsense of the reply notice, when we can't access the poster or his / her knowledge or experience? somewhat a silly occurrence.
 
Just referred to the ring diagram of 7671 and an unfused spur should only serve 1 single or double socket. That all I need to walk away
 
Last edited by a moderator:
He’s a cheeky t#at that boss of yours if he has actually dumped this on you and expects you to certify it.
Is he actually aware of how it has been installed?
Probably don't know what BS7671 refers to.
 
You shouldn’t have to alter or install anything as you have not installed it , only signing it off as compliant with bs7671, so to me you have only one option, refuse to certify it.
Tell your boss to do it, as he’s the one who said his company will certify it.
Of course he should. Not so simple with a with a such a good so boss.
 

Reply to 4mm radial from ring feeding CUs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
690
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hello all. I have just bought my first house but it needs a bit of work. I am re-wiring it and I've found the conservatory ring has been spurred...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top