Search the forum,

Discuss 5 amp Radial Bs1363 Socket in the UK Electrical Forum area at ElectriciansForums.net

J

john100

Hi

I have a Radial circuit wired with 2.5mm T&E , which is protected by a 3 amp MCB due to the fact that it is switched via a home automation relay rated at 5amp.

My question is this

Given the above scenario is it ok to install/wire a BS1363 socket if I know that the load that will be plugged in will be less than 3amp or do I have to fuse down with an FCU to stop a 13amp load which may be plugged in by the home owner. If I label the socket accordingly would this be acceptable

J
 
As already mentioned , not worth any other fusing with the MCB rating that your installing , you won't get any discrimination …….
 
Thanks for the advice

Just out of interest , is there any situation where installing a BS1363 socket is not allowed on a radial circuit for circuits rated at less than 13 amp.

I.e would it be acceptable to have a 6 amp MCB 1.5mm T&E Radial protected circuit that uses BS1363 sockets without labelling them

J
 
I've got a stash of 3's and 4's as they're useful for making up heating control systems
 

Reply to 5 amp Radial Bs1363 Socket in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top