Discuss 5 flats....1 EICR?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

L

LlandrilloSpark

Evening fella's, I'm doing a building tomorrow which contains 5 one bed flats, the building is number 1 on the street, would one EICR surfice, defects could be split into the different flats , or should I do 5 EICR's!
 
If each flat has it's own CU/DB then it's individual ones. If it's one covering the whole lot then one EICR should cover it.
 
Bit different but I've just done an office block, all one company. 4 floors each with own meter plus meter for landlord/communal. i did 5 individual reports.
 
If they have their own supply or split supply (service block after meter) they are considered as a separate installation and need their own eicr, if there are more than one cu but they are supplied from a cu on the same supply further up the system then you can use continuation sheets for the same eicr,

with a it's own supply you will have a different ze pfc and possibly tails, earth and bonding sizes and main switch, all which have their own condition report on the last few pages of the report


Loadsa paperwork!!!!
 
Building turned out to be 3 phase , 5 flats and a communal hallway, some flats had 2 CU 's because of the add ons, in total there was 11 CCU's! Covering the 6 reports that need doing, plenty of issues as you would expect.

I inspected 50% of all accessories, IR to earth all circuits in parallel, R2, ZS and RCD where required

Out of interest what would you charge
 

Reply to 5 flats....1 EICR?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
893
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock