    Hi guys
    I have had an issue with a couple of sockets in a property when carrying out ELI tests on them saying greater than 50v and won't let me test, some sockets are ok on the same circuit just a couple saying this anybody come across this and understand what it means,I'm using a megger and the system is TNCS
     
  2. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you checked the sockets internal connections sounds like loss of earth continuity.
     
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    loss of earth should bring up the N-PE indicator on a megger. @OP are you sure the MFT indicated > 50V and not < 50V.
     
    • Agree Agree x 3
  4. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Not used one of these testers but often a 50v warning indicates a continuity problem.
     
    • Agree Agree x 1
  5. Sb8389
    Offline

    Sb8389 Regular EF Member

    Location:
    Nottingham
    Yea greater which is confusing I have done two probe test with no issue at all only happens with 3 lead test
     
  6. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you retried the sockets which are okay.
     
    • Like Like x 1
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    sounds weird to me. when performing EFLI test, you should have > 50V, should be 240V. unless it's saying >50V N-E, which could indicate an earth fault.
     
    • Agree Agree x 2
  8. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Think that's what he's saying tel, greater than 50v on the Earth.
     
  9. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you physically checked to the socket terminals to verify continuity and polarity, if this is okay the socket could have internal corrosion so swap it and retry.
     
    • Agree Agree x 2
  10. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    On my old Megger seperate it means phase neutral reversed or no earth connection .Also excessive voltage between N+E.
    I suppose megger have kept the same convention
     
  11. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    the megger mft's have 3 voltage indicators. L-N, L-E and N-E. the first 2 light in normal circumstances, the 3rd only if there is a finite voltage seen N-E and the tester refuses to test.
     
  12. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Excessive voltage between N/E generally means no earth.
     
    • Agree Agree x 1
  13. Sb8389
    Offline

    Sb8389 Regular EF Member

    Location:
    Nottingham
    Just retested the sockets and all testing ok only since I found a neutral to earth fault on the leg back to mains and disconnected it not sure how this would affect the issue I have had
     
  14. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    @westward10@westward10 It does on mine , along with the others.
     
  15. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you totally isolated the faulty part or just disconnected from the board because if it is the latter the fault would still be there on a ring final.
     
Loading...
Similar Threads - >50v megger doing Forum Date
For Sale [South]: Megger PDA1 Power disturbance analzyer for spares / repair For Sale and Wanted Forum Apr 8, 2018
Megger LT320&RCDT310. Function Query from a student. Electrical Forum Mar 23, 2018

Share This Page

Users found this page by searching for:

  1. eli tester

Electricians Directory Post a Domestic Job Post a Commercial Job