Discuss >50v on megger when doing ELI test in the Electrical Forum area at ElectrciansForums.co.uk.

Tags:
Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Sb8389
    Offline

    Sb8389 Regular EF Member

    Location:
    Nottingham
    Hi guys
    I have had an issue with a couple of sockets in a property when carrying out ELI tests on them saying greater than 50v and won't let me test, some sockets are ok on the same circuit just a couple saying this anybody come across this and understand what it means,I'm using a megger and the system is TNCS
     
  2. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you checked the sockets internal connections sounds like loss of earth continuity.
     
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    loss of earth should bring up the N-PE indicator on a megger. @OP are you sure the MFT indicated > 50V and not < 50V.
     
    • Agree Agree x 3
  4. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Not used one of these testers but often a 50v warning indicates a continuity problem.
     
    • Agree Agree x 1
  5. Sb8389
    Offline

    Sb8389 Regular EF Member

    Location:
    Nottingham
    Yea greater which is confusing I have done two probe test with no issue at all only happens with 3 lead test
     
  6. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you retried the sockets which are okay.
     
    • Like Like x 1
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    sounds weird to me. when performing EFLI test, you should have > 50V, should be 240V. unless it's saying >50V N-E, which could indicate an earth fault.
     
    • Agree Agree x 2
  8. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Think that's what he's saying tel, greater than 50v on the Earth.
     
  9. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you physically checked to the socket terminals to verify continuity and polarity, if this is okay the socket could have internal corrosion so swap it and retry.
     
    • Agree Agree x 2
  10. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    On my old Megger seperate it means phase neutral reversed or no earth connection .Also excessive voltage between N+E.
    I suppose megger have kept the same convention
     
  11. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    the megger mft's have 3 voltage indicators. L-N, L-E and N-E. the first 2 light in normal circumstances, the 3rd only if there is a finite voltage seen N-E and the tester refuses to test.
     
  12. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Excessive voltage between N/E generally means no earth.
     
    • Agree Agree x 1
  13. Sb8389
    Offline

    Sb8389 Regular EF Member

    Location:
    Nottingham
    Just retested the sockets and all testing ok only since I found a neutral to earth fault on the leg back to mains and disconnected it not sure how this would affect the issue I have had
     
  14. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    @westward10@westward10 It does on mine , along with the others.
     
  15. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Have you totally isolated the faulty part or just disconnected from the board because if it is the latter the fault would still be there on a ring final.
     
Loading...
Similar Threads - >50v megger doing Forum Date
fluctuating resistants reading megger met 1710 Electrical Tools and Products Aug 25, 2018