Testing today. Zs produced an Err 4 reading on the Fluke MFT, so I got the wander lead out and connected to the MET. No continuity but 60 (ish) volts difference showing on the display.

Any ideas?
 
Sounds like there’s no earth continuity on the circuit. Was the circuit live when you tested with wander lead? The 60v is likely to be an induced or floating voltage on the unearthed conductor.
 
There’s no earth at that point in the circuit plus something has caused a potential of 60 volts to earth to appear on the earth terminal at that point.
I assume this is an EICR since you have carried out the efli test before the continuity of cpc so you need to code it accordingly.
 
It's actually a minor works. Intending to extend lighting circuit from that point.

Looks like I'll be spending my Saturday looking for a missing CPC. Oh joy.

My top tip for you .... Doing a Zs at the point you wish to extend from .... And make 100% sure any pricing you give allows for unexpected issues arising and you can charge the client more ...
 
My top tip for you .... Doing a Zs at the point you wish to extend from .... And make 100% sure any pricing you give allows for unexpected issues arising and you can charge the client more ...

It's a longstanding client luckily so it's all day rate.

Found the issue, broken CPC in a pendant, possibly moved by a decorator. (Not that I'm pointing fingers).

It wasn't the lack of earth continuity that puzzled me so much as the 60V.
 
with a broken cpc , it's common to read a voltage on the part of the cpc that is not connected. commonly known as a floating voltage. could be induced from current carrying cables in close proximity. once the cpc has been repaired, that voltage will be like Donald Trump's personality. totally disappeared.
 
A very conveniently round mft Figure .(on a secondary display ?)
Warning of danger rather than acuracy !
( High input resistance of mft lets it get that high )
- would be lower if you put your finger there -
( not a suggestion ! )

Never should have moved from needles to LCD...
Although,of course,this may have dulled the enjoyment,of an Xbox:)
 

Reply to 60 volts on an R2 long lead test? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
824
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
Hi folks. Im a RECI contractor based in Co Sligo, Ireland . I was doing erroneous testing on a domestic board which gave me readings between 90V-...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock