Discuss 6mm cooker cable in the UK Electrical Forum area at ElectriciansForums.net
Cable overload protection also depends on the installation method. Here, probably on dodgy territory.
Cable fault protection comes down to the circuit characteristics and if that meets the adiabatic limit for a given cable. Here, almost certainly.
The cooker rating does come in to it. If the absolute max of the cooker (plus any 13A socket) is less than, say, 32A limit for your typical 6mm in the majority of install methods, then all you need is fault protection. But more generally cookers will exceed that max value and you get away with it due to diversity - that typical usage never has all on max for any length of time, but you cannot use diversity for overload protection (only for circuit sizing) as it is possible to overload, so your RCBO must protect against that scenario.
TL;DR 40A is on the high side unless cable is known to be freely ventilated on whole length. Check OSG for methods and corresponding ratings.
So if there was no socket you would stick that on a 20amp?cooker diversity says:
10A + 30% of remainder (+5A if socket integral).
e.g . 10kW total rating = 42A. so
10A + (30% of 32A) = 10 + 9.6 = 19.6A. add the 5A for socket if needed. = 24.6A.
32A MCB/RCBO and 6.0mm is good unless loads of insulation.
fault protection is a differemt kettle of kippers.
Generally no. But you could if pushed and there was some bizarre reason to justify do so.So if there was no socket you would stick that on a 20amp?
Thanks mate, everything is easy enough just cooker and showers, but ill get this book tomorrow may come in handy.The OSG Appendix A has the various diversity guidance to use for different situations (e.g. commercial kitchen) but it is far from obvious just how.
The IET's "Electrical Installation Design Guide" has some worked examples, so if you can afford it I would suggest getting a copy as it helps illustrate a lot of these examples.
Thanks mate, everything is easy enough just cooker and showers, but ill get this book tomorrow may come in handy.
I've got the 2391-52 18th edition. I'm nearly completed level 3. I'm just wanting to become a good electrician that does things by the book mate.Didn't you say you were doing EICRs?
I've got the 2391-52 18th edition. I'm nearly completed level 3. I'm just wanting to become a good electrician that does things by the book mate.
No need to panic yourself mate.Sorry, I might have got it wrong. I thought you were carrying out condition reports.