Sb8389

-
Reaction score
25
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

thanks.
 
8.5KW is about 37A which is approx 1.16 times the MCB rated current. I don't have a chart but the trip time will be hours and depending on the ambient temperature it might never trip so you're looking at a lot longer than it takes to have a shower.
 
Thanks marvo,
It's just my boss is saying it is non compliant as the In is greater than Ib and is therefore a risk and can't be left in place with us doing a board change and that I would need to rewire it in 10mm if they want to keep the shower, I didn't agree with him so wanted an experts opinion on the scenario.
 
It is non compliant because the regulations require circuits to be designed such that they are not subject to small overloads.

And 35.4 is greater than 32 ;)
 
Thanks marvo,
It's just my boss is saying it is non compliant as the In is greater than Ib and is therefore a risk and can't be left in place with us doing a board change and that I would need to rewire it in 10mm if they want to keep the shower, I didn't agree with him so wanted an experts opinion on the scenario.


My 8.5Kw shower has been running on a B32 60898 since i moved in to my flat 9 years ago and has not tripped once while taking a shower.

Just a thought. :)
 
Surely I could just write this in the departures on the certificate as I have not installed the circuit. Surely It's not going to be a risk like my boss is making out and like marvo says the chances of it tripping are very slim.
 
It is non compliant because the regulations require circuits to be designed such that they are not subject to small overloads.

And 35.4 is greater than 32 ;)


Would it be classed as overload if the cable is rated to carry the current even though the mcb is rated marginally less?

Not saying that this is the case here, I'd guess the cable is genuinely overloaded if it's buried under insulation.
 
Would it be classed as overload if the cable is rated to carry the current even though the mcb is rated marginally less?

Not saying that this is the case here, I'd guess the cable is genuinely overloaded if it's buried under insulation.

Is a 32A mcb with 35A flowing through it subject to a small overload?
 
My 8.5Kw shower has been running on a B32 60898 since i moved in to my flat 9 years ago and has not tripped once while taking a shower.

Just a thought. :)

Remind me which regulation number it is which says that something which has worked for 9 years is automatically considered correct and other regulations can be ignored?
 
Remind me which regulation number it is which says that something which has worked for 9 years is automatically considered correct and other regulations can be ignored?
Hi davesparks,
would you say the circuit needs rewiring then,I know the circuit has being designed incorrectly but does it mean it's a risk or just not compliant to regs and can be just noted on cert.
 
No it's not, it's rated to break a fault current of up to 10kA, it's rated for an operating current of 32A
It's also rated for an operating current of 35A for a specific duration of time. I guess our definition of 'overload' might be differing slightly.
 
Remind me which regulation number it is which says that something which has worked for 9 years is automatically considered correct and other regulations can be ignored?


I never said it was correct or compliant. But to be honest It was installed by the housing associations so called sparks so i wouldn't expect it to be to be honest.

My point was simply that it wont trip while taking a shower unless your in there for a very very very long time.
 
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

thanks.

This is a interesting thread! I wonder how many times a consumer unit is changed that has an 8.5KW shower on a 6mm, quite often I expect. A 6mm cable is fine for 8.5KW shower (if clipped direct), but when we change a consumer unit how are we to tell if the walls have insulation in them (ref method 102) and if the cable is not touching the inner wall (ref method 103)?

If you have these details SB then I cant really see how you can reconnect back up given that the CCC of the cable is going to be anywhere from 23.5A (ref method 103) to 34A (ref method 100). Although if it is ref method 100 (34A) then even though a 32A MCB will not trip at 34A I would have thought the CCC of cable (with regards ref method) is designed with this in mind.
 
I see your point happyhippydad but to determine how it's installed throughout its length can be difficult in a lot situations.
it was installed on 30amp before and there is no evidence of overheating to the cable. I know that don't confirm its right to leave it but does that mean we have say to the customer it will need rewiring when we come across this situation when we can't determine its installation method.
 

Reply to 8.5kw Shower on a 6.0mm cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
738
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
433
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
806
At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock