Currently reading:
8.5kw Shower on a 6.0mm cable

Discuss 8.5kw Shower on a 6.0mm cable in the UK Electrical Forum area at ElectriciansForums.net

Sb8389

-
Reaction score
25
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

thanks.
 
8.5KW is about 37A which is approx 1.16 times the MCB rated current. I don't have a chart but the trip time will be hours and depending on the ambient temperature it might never trip so you're looking at a lot longer than it takes to have a shower.
 
Thanks marvo,
It's just my boss is saying it is non compliant as the In is greater than Ib and is therefore a risk and can't be left in place with us doing a board change and that I would need to rewire it in 10mm if they want to keep the shower, I didn't agree with him so wanted an experts opinion on the scenario.
 
Thanks marvo,
It's just my boss is saying it is non compliant as the In is greater than Ib and is therefore a risk and can't be left in place with us doing a board change and that I would need to rewire it in 10mm if they want to keep the shower, I didn't agree with him so wanted an experts opinion on the scenario.


My 8.5Kw shower has been running on a B32 60898 since i moved in to my flat 9 years ago and has not tripped once while taking a shower.

Just a thought. :)
 
Surely I could just write this in the departures on the certificate as I have not installed the circuit. Surely It's not going to be a risk like my boss is making out and like marvo says the chances of it tripping are very slim.
 
It is non compliant because the regulations require circuits to be designed such that they are not subject to small overloads.

And 35.4 is greater than 32 ;)


Would it be classed as overload if the cable is rated to carry the current even though the mcb is rated marginally less?

Not saying that this is the case here, I'd guess the cable is genuinely overloaded if it's buried under insulation.
 
Remind me which regulation number it is which says that something which has worked for 9 years is automatically considered correct and other regulations can be ignored?
Hi davesparks,
would you say the circuit needs rewiring then,I know the circuit has being designed incorrectly but does it mean it's a risk or just not compliant to regs and can be just noted on cert.
 
Remind me which regulation number it is which says that something which has worked for 9 years is automatically considered correct and other regulations can be ignored?


I never said it was correct or compliant. But to be honest It was installed by the housing associations so called sparks so i wouldn't expect it to be to be honest.

My point was simply that it wont trip while taking a shower unless your in there for a very very very long time.
 
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

thanks.

This is a interesting thread! I wonder how many times a consumer unit is changed that has an 8.5KW shower on a 6mm, quite often I expect. A 6mm cable is fine for 8.5KW shower (if clipped direct), but when we change a consumer unit how are we to tell if the walls have insulation in them (ref method 102) and if the cable is not touching the inner wall (ref method 103)?

If you have these details SB then I cant really see how you can reconnect back up given that the CCC of the cable is going to be anywhere from 23.5A (ref method 103) to 34A (ref method 100). Although if it is ref method 100 (34A) then even though a 32A MCB will not trip at 34A I would have thought the CCC of cable (with regards ref method) is designed with this in mind.
 
I see your point happyhippydad but to determine how it's installed throughout its length can be difficult in a lot situations.
it was installed on 30amp before and there is no evidence of overheating to the cable. I know that don't confirm its right to leave it but does that mean we have say to the customer it will need rewiring when we come across this situation when we can't determine its installation method.
 
I see your point happyhippydad but to determine how it's installed throughout its length can be difficult in a lot situations.
it was installed on 30amp before and there is no evidence of overheating to the cable. I know that don't confirm its right to leave it but does that mean we have say to the customer it will need rewiring when we come across this situation when we can't determine its installation method.

Very true SB! But you've said in your post that its covered in insulation, so you have determined how its installed. If its got >100mm of insulation over it in the loft which is quite feasible then its CCC goes down to 27! I suppose you could clamp it and see how much it is drawing and perhaps use a 25A MCB? But you could start getting some tripping!
 
Very true SB! But you've said in your post that its covered in insulation, so you have determined how its installed. If its got >100mm of insulation over it in the loft which is quite feasible then its CCC goes down to 27! I suppose you could clamp it and see how much it is drawing and perhaps use a 25A MCB? But you could start getting some tripping!

How on earth would a lower rated mcb help the situation?
The mcb does not determine the load current!
 
Very true SB! But you've said in your post that its covered in insulation, so you have determined how its installed. If its got >100mm of insulation over it in the loft which is quite feasible then its CCC goes down to 27! I suppose you could clamp it and see how much it is drawing and perhaps use a 25A MCB? But you could start getting some tripping![/Q

i will clamp it tomorrow and see what its drawing and give myself a clearer idea of what we are dealing with.
 
How on earth would a lower rated mcb help the situation?

It converts a 'possible cable overheating' risk into a 'shower user jumps out of cold shower and goes to reset MCB with wet hands' risk. I've lost track, was this thread about solving a problem or creating one?
 
How did you get to 37A from an 8.5kW shower?
A 40A mcb would be correct for the load

I think you may be trying to push me towards saying the obvious here :smile5:

How on earth would a lower rated mcb help the situation?
The mcb does not determine the load current!

The OP has stated the reference method. i.e 'covered in insulation', so the CCC of the cable is reduced, would you suggest increasing the MCB?
 
Last edited:
Operating current was a poor choice of words in this case.
I don't think it will be rated to operate at 35A at all.
According to the published curves all MCB's are designed to be operated above their In and perform to the predictable disconnect times which in this case, given it's a fixed load and a disconnect time far in excess of the duration of use, will not be of consequence. I think it's a stretch to say this particular circuit is overloaded just because the load is 1.16 times the In and assuming the cable size is appropriate.
 

Reply to 8.5kw Shower on a 6.0mm cable in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock