8.5kw Shower on a 6.0mm cable

Discuss 8.5kw Shower on a 6.0mm cable in the UK Electrical Forum area at ElectriciansForums.net

Sb8389

-
Reaction score
25
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

thanks.
 
Agreed - we know it's non-compliant - but it raises the question: is it dangerous to have In<Ib when in practice we know it 'never' trips? Especially if In<Iz so the cable is theoretically protected.
 
Actually a 25A MCB will probably not trip at 37A or at least take a couple of hours (looking at the tables), so this could be your answer to the lower CCC of the cable due to reference method!
 
I think you may be trying to push me towards saying the obvious here :smile5:



The OP has stated the reference method. i.e 'covered in insulation', so the CCC of the cable is reduced, would you suggest increasing the MCB?

The obvious here is that the mcb is too small for the load, the only soloution to that is a bigger mcb.

The rating of the mcb will have no bearing on the load current which flows when the shower is operating. It is an 8.5kW load, whatever the mcb is rated at it will draw 35.4A at 240V
Of you fit a lower rated mcb it will just operate faster!
 
Sure, but follow the twisted logic here. Suppose the cable has an Iz that on paper is inadequate. It is protected by an MCB having In<Iz. This means In is also inadequate, but suppose also that we know from the curves that it will never trip. Is the cable overloaded?
 
Agreed - we know it's non-compliant - but it raises the question: is it dangerous to have In<Ib when in practice we know it 'never' trips? Especially if In<Iz so the cable is theoretically protected.
This is where I was going but you put it better than I could. I guess the question in the UK would be how would you code it or would you even code it if you were doing an EICR type inspection? I personally couldn't class this as dangerous in any way and I'd be hard pushed to even say it needed improvement from a purely technical viewpoint.
 
Sure, but follow the twisted logic here. Suppose the cable has an Iz that on paper is inadequate. It is protected by an MCB having In<Iz. This means In is also inadequate, but suppose also that we know from the curves that it will never trip. Is the cable overloaded?

If the Iz is inadequate then that implies it is less than the load current so yes it is overloaded.
 
This is where I was going but you put it better than I could. I guess the question in the UK would be how would you code it or would you even code it if you were doing an EICR type inspection? I personally couldn't class this as dangerous in any way and I'd be hard pushed to even say it needed improvement from a purely technical viewpoint.

Then what is the point of having the ratings that we do have?
 
....Still need to clamp it,regardless of what it says on the tin...have a concrete fact,to apply the theory to...if you clamped three units of the same stated size,especially if of vintage,you would get three different values,and possibly three separate ways forward,bearing in mind the fractional amounts discussed.

...8.5Kw?...that bus had "Kelloggs" wrote on the side of it...but it wasn't full of cornflakes :crazy:
 
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40A MCB but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

thanks.
It would be a risk to swap it to 40A MCB without changing the cable or moving it out of the insulation as the MCB would then be rated higher than the cable's current carrying capacity in insulation.

The MCB already looks to be higher rated than the cable rating when completely enclosed in insulation. It's probably not been an issue because showers only tend to be used for 10-15 minutes at a time, but leave it on for long enough and that cable could well be in trouble.
 
Last edited:
Lets not forget that an MCB can handle 1 & 1/2 times it rating for up to an hour!

Clamp it, do the cable calcs for the installation method and if the the load is too much for the cable, rewire it or reduce the load/change the shower unit.

As for coding, code 3 before investigation and then code 2 once you can see the install is incorrect (going by the info in this thread).
 
Basic cable calcs, check the regs book to see if it complies, if it doesn't which in this case it appears not to, it does not meet BS7671 which are the regulations you as a registered electrician are employed by the customer/client etc to work to and ensure all that you do meets these standards, it is the whole point of the game. If you choose to ignore the regs then why bother being registered at all, just connect it all up, if it doesn't go bang, job done? Or let the customer know what the issue is, quote for rectifying the issue, if they choose not to take your advice and don't proceed with the works, issue a dangerous situation report and walk away.
 
Last edited by a moderator:
The obvious here is that the mcb is too small for the load, the only soloution to that is a bigger mcb.

The rating of the mcb will have no bearing on the load current which flows when the shower is operating. It is an 8.5kW load, whatever the mcb is rated at it will draw 35.4A at 240V
Of you fit a lower rated mcb it will just operate faster!

When designing or using calculations we should be using 230V.

It will operate faster, but a 32A MCB with 37A flowing through it will not operate.
 
in far less time than it's taken to read this thread, i'd have had the cable out of the insulation, with said insulation being consigned to the bin. no cost, installation compliant, down the pub.
 
It would be a risk to swap it to 40A MCB without changing the cable or moving it out of the insulation as the MCB would then be rated higher than the cable's current carrying capacity in insulation.

The MCB already looks to be higher rated than the cable rating when completely enclosed in insulation. It's probably not been an issue because showers only tend to be used for 10-15 minutes at a time, but leave it on for long enough and that cable could well be in trouble.

What is wrong with the mcb being rated higher than the cables ccc? It only needs to be equal to or greater than the load current for a fixed load.
 
What is wrong with the mcb being rated higher than the cables ccc? It only needs to be equal to or greater than the load current for a fixed load.
agreed. overload protection is not required for a fixed load. the only problem is that the ccc of the cable is < the actual current drawn.
 
Utter rot! The shower will be rated 8.5kW at 240V not 230V so damn well calculate it at 240V
The power rating will be less at 230V.
This is basic physics you should have learned at school.
I don't think HHD's question is as stupid as you made it out and I damn well took needlework instead of physics so I have to ask the question:)

The KW rating on the appliance is a nominal value, it refers to the fact the element will give 8.5 kW of heat output at 240v. The heat output will coincide with this nominal 8.5kW figure only at this voltage, so if you drop the voltage then it's no longer a 8.5kW heater because the load current will vary proportionally to the supply voltage hence so will the heat output.

If the nominal supply voltage is 230v why would would you blindly use the nominal heat output figure given over the nominal 230v voltage figure? Why would one nominal figure be preferable to use over another nominal reference figure?
 
Last edited:
I don't think HHD's question is as stupid as you made it out and I damn well took needlework instead of physics so I have to ask the question:)

The KW rating on the appliance is a nominal value, it refers to the fact the element will give 8.5 kW of heat output at 240v. The heat output will coincide with this nominal 8.5kW figure only at this voltage, so if you drop the voltage then it's no longer a 8.5kW heater because the load current will vary proportionally to the supply voltage hence so will the heat output.

If the nominal supply voltage is 230v why would would you blindly use the nominal heat output figure given over the nominal 230v voltage figure? Why would one nominal figure be preferable to use over another nominal reference figure?

If the supply voltage genuinely is 230V then use the 230V power rating, it will be written on the damn data plate for both voltages.
Go in to B&Q and look at the showers, they have power input at both 240V and 230V these days.

Older appliances will only have a 240V rating so you should use 240V in your calculation otherwise you are introducing an error into your calculation to begin with.
 
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

How long is the run of 6mm2 between mcb and shower?
 
If the supply voltage genuinely is 230V then use the 230V power rating, it will be written on the damn data plate for both voltages.
Go in to B&Q and look at the showers, they have power input at both 240V and 230V these days.

Older appliances will only have a 240V rating so you should use 240V in your calculation otherwise you are introducing an error into your calculation to begin with.

So if they are rated at 8.5kW at 240V and the damn supply voltage in the UK is 230V are you saying that you would still base your damn current on 240V?

Also, I'm a little concerned that you have suggested to the damn OP to increase the damn MCB to 40A given the damn reference method (covered in insulation). Would you still suggest he increases the damn MCB to 40A?
 
Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.

How long is the run of 6mm2 between mcb and shower?

Its about 15 metres max pal
 
So if they are rated at 8.5kW at 240V and the damn supply voltage in the UK is 230V are you saying that you would still base your damn current on 240V?

Also, I'm a little concerned that you have suggested to the damn OP to increase the damn MCB to 40A given the damn reference method (covered in insulation). Would you still suggest he increases the damn MCB to 40A?

Bleedin' 'ell........we've all gone hydro.....dams all over the place
 
soon fix them dams:


is (1).jpg
 
Put the Damn handbags away Godammit.:)
 
Sorry if this has already been posted up but I'm tired and only skim read the 4 pages worth on this - wouldn't the most practical and easy solution be to see if there's a bit of slack on the 6mm in the loft and if so just lift the cable up and clip it /otherwise secure it above the insulation ? This would greatly reduce the risk of overheating - and I'd leave it on a 32a MCB as well, in the real world there will be no issues.
I worked with a bloke years ago who had the shower at home through a B16- to stop his teenage kids being in there too long and costing too much with the leccy. This fella is also a Yorkshireman which is purely coincidental. :) No damn damns from me.
 

Reply to 8.5kw Shower on a 6.0mm cable in the UK Electrical Forum area at ElectriciansForums.net