Discuss 8 way CU with 17 circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

T

TPES

What's your thoughts on EICR code?

It's all lighting, 8 x 6a MCB's some MCBs have 4 or 5 1-1.5mms twisted into the top of them, nothing labeled up correctly as can't fit info for all circuits onto the board.. Circuits not actually overloaded just way to overcrowded in the board. Finding it impossible to test

What code would you give?
 
^^^ Agree not great design, but as Murdoch says you cant code it just try to get the job to do it right.
 
Definatly no code. You really need to treat it as 8 circuits which happen to be joined at CU so as already stated not a great design. You just need to identify which is on each MCB then ZS all on that breaker and record highest reading as a single circuit, other than that it same as usual really.
 
What's your thoughts on EICR code?

It's all lighting, 8 x 6a MCB's some MCBs have 4 or 5 1-1.5mms twisted into the top of them, nothing labeled up correctly as can't fit info for all circuits onto the board.. Circuits not actually overloaded just way to overcrowded in the board. Finding it impossible to test

What code would you give?
On the testing front, turn ALL lights on, remove 3 of the 4 cables in the board and see which ones stay on (keep a note on your plan drawing) - then repeat the process for the other 3 cables - time consuming but its the way I do it!
 
You can't have multiple circuits being fed from a single point, so effectively you have 8 circuits not 17. ....No Code!!

Use Murdoch's method to locate, label and test, these multibranch lighting circuits. What you might want to check, is there the same number of corresponding neutral conductors for these lighting circuits...
 
after an argument with a qs on spuring a socket at the origin of installation
his view was its a no no as "every circuit should have its own way" im sure he did point out in the regs to me this particular line but cant recall where
 
after an argument with a qs on spuring a socket at the origin of installation
his view was its a no no as "every circuit should have its own way" im sure he did point out in the regs to me this particular line but cant recall where
er no. Many socket circuits have a spur at the board. You are correct. The QS is wrong.
 
after an argument with a qs on spuring a socket at the origin of installation
his view was its a no no as "every circuit should have its own way" im sure he did point out in the regs to me this particular line but cant recall where
While I agree that this is RAF I have to say that by the "logic" displayed by this QS it would not be compliant to spur a socket out of an MCB/RCBO if it was already feeding an RFC.
 
I think I have missed making my point after an argument (friendly) his view was that every circuit should have its own way and did point this out
the point I was trying to make was there3 is something in the regs regarding this
(I will look it up)
 
I think I have missed making my point after an argument (friendly) his view was that every circuit should have its own way and did point this out
the point I was trying to make was there3 is something in the regs regarding this
(I will look it up)

I think you may struggle to find something in 7671 regarding this.
 
It goes along the lines of "every circuit should be installed to minimise inconvenience in the event of a fault", read into that what you want, but there is nothing wrong with putting more than one circuit into one device as long as this requirement is met. from memory it is probably in part 5 of the BGB, but i don't have the inclination to go and have a look.

Cheers............Howard
 
I think I have missed making my point after an argument (friendly) his view was that every circuit should have its own way and did point this out
the point I was trying to make was there3 is something in the regs regarding this
(I will look it up)
Possibly the line and neutral conductors of each final circuit shall be separate from all other final circuits.


However multiple conductors in one device just means it is a single circuit with multiple conductors.
 

Reply to 8 way CU with 17 circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
646
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
890
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
823
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock