Covers resistance and IR, but obviously not RCD trip times and levels.
That is the aspect of my MFT I can't check myself. The closest I can do is test one of my home sockets to see it has not changed much which, while better than nothing, is not quite enough to be sure.

I have a CalCard and really would recommend it as a handy way to check the low/high R ranges. I also have other meters that can be used to verify AC volts but the Zs & RCD stuff then I only have the one MFT.
 
That is the aspect of my MFT I can't check myself. The closest I can do is test one of my home sockets to see it has not changed much which, while better than nothing, is not quite enough to be sure.

I have a CalCard and really would recommend it as a handy way to check the low/high R ranges. I also have other meters that can be used to verify AC volts but the Zs & RCD stuff then I only have the one MFT.

The Metrel Eurocheck checkbox is very good as it does RCD and Zs tests as well as the IR/resistance checks. But I've just checked the current price is nearly £350.
 
The Metrel Eurocheck checkbox is very good as it does RCD and Zs tests as well as the IR/resistance checks. But I've just checked the current price is nearly £350.
Interesting to see, a lot cheaper than the usual cal systems (they are £5k-15k I believe) but not quite enough for a single MFT, given the cal box needs cal'd as well!

If you were in a small company though it would make financial sense so 5 or so MFT could be regularly checked against it, and once a year the cal box sent out for a full check.
 
Interesting to see, a lot cheaper than the usual cal systems (they are £5k-15k I believe) but not quite enough for a single MFT, given the cal box needs cal'd as well!

If you were in a small company though it would make financial sense so 5 or so MFT could be regularly checked against it, and once a year the cal box sent out for a full check.

Exactly my thoughts. If it was under £200 I'd say everybody should have one.
 
For general info, it is Automated Calibration Services who do the CEF cal day work:
The certificates I received says they use this bit of test kit (at least for MFT/PAT use I think):
I don't see a UK price but a USA site is saying "Starting at $13,800.00" so around £11.3k
Others I see mentioned are more affordable (for a given definition of "affordable") such as this one:
Is it currently on sale at £4,209+VAT from here:
It looks less flash, so maybe less automation so not as good for quick turn-around use.

Another one I see mentioned around is this, though it is not claiming to be MFT style calibration:
Again, only a USA site coming up with a price on a quick search and they are saying it is usually sold at $22,822 so around £18.6k
 
I use a CalCard, keeping a record of last and current readings gives me what I need to know.
Didn't mention that I test RCD/RCBO's in my own home on the same socket each time, and take a note of times etc and check against last readings, but then I am retried, and only do very small works for family and friends, in fact none this year yet.
 
For general info, it is Automated Calibration Services who do the CEF cal day work:
The certificates I received says they use this bit of test kit (at least for MFT/PAT use I think):
I don't see a UK price but a USA site is saying "Starting at $13,800.00" so around £11.3k
Others I see mentioned are more affordable (for a given definition of "affordable") such as this one:
Is it currently on sale at £4,209+VAT from here:
It looks less flash, so maybe less automation so not as good for quick turn-around use.

Another one I see mentioned around is this, though it is not claiming to be MFT style calibration:
Again, only a USA site coming up with a price on a quick search and they are saying it is usually sold at $22,822 so around £18.6k
Someone mentioned "Time" offer ex demo /used once/ maybe the packaging is bashed offers to boost sales .... :)
 
What is the expected time for a MFT calibration ? is it 10 mins? 20 mins etc ????
I have no idea.

Based on my new certificate, it has 24 measurements so at 30s per test that is 12 minutes. Which is realistic but assumes the operator is familiar with that type of MFT, etc.

But I don't know if MFT have a secret test connector that would allow an automated stepping throgugh the tests and recording of results. That might take it below 5 min per instrument.
 
These calibration days I would guess as long as it takes to print off the Certificate and put some tamper stickers on it.
 

Reply to A Calibrated Question (Multi Meters) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock