- Reaction score
- 6,444
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago....
Overhead 230v lighting festoon, LED golf ball ES, zig-zagging it's way merrily down a street in Central London used for market stalls underneath. Not my installation! High vehicle managed to catch it at one point [cautionary note about cable heights over roads..] and it snapped. Down came the source end, bare copper flailing about, sparking away as it crashed into an adjacent wet wall.... and stayed live, along with all the lamps up to that point.
Why? Because of two reasons....
1) being only a standard 2c L/N festoon cable there was no earth path for an RCD to be interested in and
2) because (and at this point I am surmising) there was so much load on the circuit because this line was so long (many hundreds of metres) that whilst all the drivers in the LED lamps coped with it fine, there was so much voltage drop on the existing load already that the thermal protection in the MCB just literally didn't see what by then was a few extra watts of energy. The CPD would have been a C16, so a max Zs of around 1.10Ω-ish and I'd hazard a guess that by this point in the chain it was twenty times that at least and probably had a voltage of less than 150v.
So it seems that when ADS disconnection time is all you've got left in the protective arsenal, for safe secs size really does matter.
Overhead 230v lighting festoon, LED golf ball ES, zig-zagging it's way merrily down a street in Central London used for market stalls underneath. Not my installation! High vehicle managed to catch it at one point [cautionary note about cable heights over roads..] and it snapped. Down came the source end, bare copper flailing about, sparking away as it crashed into an adjacent wet wall.... and stayed live, along with all the lamps up to that point.
Why? Because of two reasons....
1) being only a standard 2c L/N festoon cable there was no earth path for an RCD to be interested in and
2) because (and at this point I am surmising) there was so much load on the circuit because this line was so long (many hundreds of metres) that whilst all the drivers in the LED lamps coped with it fine, there was so much voltage drop on the existing load already that the thermal protection in the MCB just literally didn't see what by then was a few extra watts of energy. The CPD would have been a C16, so a max Zs of around 1.10Ω-ish and I'd hazard a guess that by this point in the chain it was twenty times that at least and probably had a voltage of less than 150v.
So it seems that when ADS disconnection time is all you've got left in the protective arsenal, for safe secs size really does matter.
Last edited: