mattg4321

-
Esteemed
Arms
Reaction score
2,046
Just looked at a job and the storage heater has a peak and off peak supply to it. These are on different phases.

There is a label on it to warn of this. Not something I’ve seen before though and feels wrong but probably almost inevitable in commercial buildings with storage heaters.

Thoughts.
 
Its maybe impossible to reconfigure the circuits so every heater is individually on the same phase across night and day supplies.

I wonder if there was anything in the original instruction manual about it? (doubtful)

are the connections inside the heater rated for 400v, or only 230?
 
Its maybe impossible to reconfigure the circuits so every heater is individually on the same phase across night and day supplies.

I wonder if there was anything in the original instruction manual about it? (doubtful)

are the connections inside the heater rated for 400v, or only 230?

No idea. They want to me to quote to replace.

Suppose I may have to contact dimplex and ask them whether or not this is acceptable for their current storage heaters
 

Reply to A storage heater on 2 phases. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
973
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hi, My electrician removed an old Creda storage heater connected to only 1 off peak supply and installed the SSHE070 but as the power is off peak...
Replies
11
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
228

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock