Discuss Access To TT systems Earth Rod for PIR? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

T

ThomasElectric

Hello fellows,

Just wanted to get your thoughts on this...

I'm working on a property with a TT supply in the hills, I have tested the Ze at 13.5 Ohms, very healthy Earth Rod I thought. Only problem is that its been concreted over through the years so all that now exists is the earth cable with mechanical protection running into concrete outside. No sign of an earth rod anymore as its underground.

Id love to get your thoughts and the regs on this, and whether I should be putting in a new earthing rod or passing this one as its safe and sound underground, encased in concrete.

What do you think?

Daniel
 
Does anyone know for certain that it is connected to an earth rod and not, for instance, a metal utility pipe. Also you are unable to see the quality of the connection so i would think there is a case to be made for putting another rod in, or at least one in parallel - Maybe a code 3 further investigation???
 
Hello fellows,

Just wanted to get your thoughts on this...

I'm working on a property with a TT supply in the hills, I have tested the Ze at 13.5 Ohms, very healthy Earth Rod I thought. Only problem is that its been concreted over through the years so all that now exists is the earth cable with mechanical protection running into concrete outside. No sign of an earth rod anymore as its underground.

Id love to get your thoughts and the regs on this, and whether I should be putting in a new earthing rod or passing this one as its safe and sound underground, encased in concrete.

What do you think?

Daniel
if rod is unaccesible for inspection and maitenance then it does not comply with the requirements of BS 7671 i would install a new rod
 

Reply to Access To TT systems Earth Rod for PIR? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Just completed an EICR which had an Unsatisfactory Report done earlier in the year by another Spark, i have a copy of the report and he's put the...
Replies
11
Views
4K
Evening all If you were to carry out an eicr and you came across a TT system what is the procedure and required tests....I can see how you would...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock