Reaction score
1,345
Did an EICR today, generally ok, but found a FCU on the skirting board outside the bathroom that feeds a flex outlet on the skirting board in the bathroom directly behind, for a heated towel rail. The main issue was that the FCU was screwed onto the skirting board using drywall screws and there was no back box present at all. The wiring was just inside the wall void. I corrected this by adding a fastfix box on the skirting board. Did I do the right thing, or should I have insisted on moving it up?
 
As long as its safe then it,s ok after all you don,t want to be seen to be creating unnecessary work,that just makes you look like a cowboy.These days honesty and fairness will take you a long way,after all you never know who,s coming in after you.well done.
 
There tends to be a myth flying about that accessories mounted on skirtings is not allowed and illegal. There is nothing stated in bs7671 to back this misinterpretation. The only things that needs to be taken into account are
a) Is the equipment suitable for the external conditions and influences where it is installed?
b) Is there a likelihood that the accessory will be exposed to the risk of mechanical damage i.e hoovers, furniture etc.
 
There tends to be a myth flying about that accessories mounted on skirtings is not allowed and illegal. There is nothing stated in bs7671 to back this misinterpretation. The only things that needs to be taken into account are
a) Is the equipment suitable for the external conditions and influences where it is installed?
b) Is there a likelihood that the accessory will be exposed to the risk of mechanical damage i.e hoovers, furniture etc.

and don't forget that there has to be no risk of appliances being plugged into a skirting socket having its lead bent in such a way as to cause damage.
(Not relevant in this case)
 
One has to remember that in years gone by, skirting boards could be 14'' or more high. I remember re-wiring all the socket outlets at an old friend of mines parents Victorian house, where all the socket outlets went into those massive skirting boards. They were over an inch thick too!! lol!!
 
Only time heights come into it is when Disability Discrimination Act rules apply then its min 450AFFL to bottom and 1200 AFFL to to top for switches, the regs do not cover this topic only Disability Discrimination Act rules apply
 
Only time heights come into it is when Disability Discrimination Act rules apply then its min 450AFFL to bottom and 1200 AFFL to to top for switches, the regs do not cover this topic only Disability Discrimination Act rules apply

not quite when its a new build height rules apply under part P have a look at the electricians guide to the building regs
 
not quite when its a new build height rules apply under part P have a look at the electricians guide to the building regs

This falls under building reg Part M, if you comply with Part P, then by default you will also comply with Part M and all the rest of them.

Cheers...........Howard
 

Reply to Accessories on skirting board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hello all, Just some advice... I am fitting insulating boards on an external wall in a bedroom (50mm thick with plasterboard) as the end terrace...
Replies
5
Views
4K
Looking to see where I went wrong and see why I made a mess of things. I was asked to install a Hive onto a Vokera Vision 30C combi boiler. I...
Replies
19
Views
6K
Slightly tongue in cheek title, but with all of the recent EICRs I've done, the new build flats built between 10-20 years old seem to cause the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock