Octopus

OK - this is a dual board, about 3 years old ......... 1 RCD per bank.

They are experiencing random tripping, and my trusty earth leakage clamp shows that both banks are running at around 21 mA leakage - so the smallest change plunges half the house into darkness etc.

Anyone know if I could easily source the parts to add 2 more RCD's (yes I realise some circuit consolidation would be required ....

Hager dual CU.jpg


Thanks

And no I didn't install this!
 
The client did ask what the best solution was - I said replace ALL the MCB's with RCBO's but with 26 circuits this wouldn't be cheap!
I think that will be the only option as there is not any space to fit a two modular RCD to make each board split RCD.
 
The cheapest place i have found recently for hager rcbos is
discount-electrical.co.uk also known as shop4electrical.
The price can vary widely between suppliers. Hager are good with 2 year warranty too in event of failures. Dodgy batc etc...just never buy direct from hager though. They charge the list price!
 
Even if you manage to split that lot over an extra couple of RCD's there's no assurance that nuisance tripping of a bank of circuits will not be a regular occurrence. The client will likely assume that whatever you do will be a total cure.
I'd insist on fitting RCBO's regardless of cost.
 
I had the same issue on a stackable Hager 36 way board. Lots of electronics and control system were leaking due to design.

We added another neutral bar and put rings, cooker and kitchen on rcbo's. Problem went away, I think adding an RCD would be more hassle than it's worth.
 
How does adding another neutral bar solve the problem ?
The only thing that makes sense is that it lowers the neutral systems impedance.
In which case that indicates a failing or poor neutral system to start with.
 

Reply to Adapt this CU........... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K
Q1: I am not far off getting professional in but which professionals and how to find a good one? I have researched and investigated a bit myself...
Replies
14
Views
4K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Done an EICR this week on a small flat, no issues other than the CU, E-line dual RCD, plastic, roughly 10 years old. MCBs didn't seem to sit right...
Replies
0
Views
673

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock